Old 05-30-2007, 11:24 AM
Restricted, crimped air ducts?
Old 05-30-2007, 04:25 PM
DavidR's Avatar
DavidR DavidR is offline
Re: Restricted, crimped air ducts?
Jeff,
It wouldn't be a bad idea to recommend that they have the static pressure of the duct system tested to verify proper airflow.
Any equipment attached to a duct system like that is in for a rough run.
Old 05-30-2007, 04:34 PM
DavidR's Avatar
If you need a contractor in Vegas that does performance testing I can hook you up Jeff.
One of the guys who mentored me lives in Vegas.
Old 06-01-2007, 10:42 AM
Joseph Rago Joseph Rago is offline
As a rule, flexible ductwork should not be installed in lengths greater than 8 feet, and with a bend greater than 90 degrees. One could test for "static pressure", but where? Suggest testing for volume delivered at each outlet for a more definitive result.
Joseph D. Rago P.E.
A.E.G.
Yardley PA
Old 06-01-2007, 03:46 PM
DavidR's Avatar
You could test the total external static pressure to see how much resistance the fan is seeing & you could also measure the static pressure drop of each suspect flex run out.
Most guys can afford a manometer or magnehelic, most don't have anyway of measuring air volume from the registers.
  #6 (permalink)
Old 06-01-2007, 09:37 PM
Quote:
Where is that information from?
Would like to read it.
I know that flexible "air connectors" are not allowed longer than 14 feet, but "flexible duct" length is unlimited.
Thanks.
  #7 (permalink)
Old 06-01-2007, 10:00 PM
Rick Hurst's Avatar
Rick Hurst Rick Hurst is online now
Why not install saddles below the ducts where the strap is restricting the air flow?
Similar Threads
Air ducts John Stephenson Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 2 05-08-2007 06:22 PM
Metal ducts Jeff Eastman Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 5 04-07-2007 03:12 AM
vB.Sponsors