Ron, I think there was a thread on this not too long ago, do a search in HVAC. Found it. Read #7.
- M1601.1.1 Above-ground duct systems. Above-ground duct systems shall conform to the following:
- - 1. Equipment connected to duct systems shall be designed to limit discharge air temperature to a maximum of 250°F (121°C).
- - 2. Factory-made air ducts shall be constructed of Class 0 or Class 1 materials as designated in Table M1601.1.1(1).
- - 3. Fibrous duct construction shall conform to the SMACNA
Fibrous Glass Duct Construction Standards or NAIMA Fibrous Glass Duct Construction Standards.
- - 4. Minimum thickness of metal duct material shall be as listed in Table M1601.1.1(2). Galvanized steel shall conform to ASTM A 653.
- - 5. Use of gypsum products to construct return air ducts or plenums is permitted, provided that the air temperature does not exceed 125°F (52°C) and exposed surfaces are not subject to condensation.
- - 6. Duct systems shall be constructed of materials having a flame spread index not greater than 200.
- - 7. Stud wall cavities and the spaces between solid floor joists to be used as air plenums shall comply with the following conditions:
- - - 7.1. These cavities or spaces shall not be used as a plenum for supply air.
- - - 7.2. These cavities or spaces shall not be part of a required fire-resistance-rated assembly.
- - - 7.3. Stud wall cavities shall not convey air from more than one floor level.
- - - 7.4. Stud wall cavities and joist-space plenums shall be isolated from adjacent concealed spaces by tight-fitting fire blocking in accordance with Section R602.8.