Old 09-27-2007, 08:16 PM
Jim Luttrall Jim Luttrall is online now
Condensate switch
Anybody know if these are supposed to be in the primary drain line?
I see them pretty regularly in the secondary drain as a plug, but I have never seen the flow through design.
Thanks, Jim
Mr. Inspector.net, Inc.
Allen, Texas 75002
Home inspection
Old 09-27-2007, 08:52 PM
Re: Condensate switch
Besides that plastic being close to the draft hood, which requires 6" clearance to combustible material (plastic is a combustible material, as is the insulation on the conductor from the switch), and that there is no trap there ...
*IF* that meets UL 508, it is allowed there, "sort of" (see below).
M1411.3.1 Auxiliary and secondary drain systems.
- 4. A water level detection device conforming to UL 508 shall be provided that will shut off the equipment served in the event that the primary drain is blocked. The device shall be installed in the primary drain line, the overflow drain line or the equipment-supplied drain pan, located at a point higher than the primary drain line connection and below the overflow rim of such pan.
The "sort of" catch - read the underlined section.
While I think these are worthless at preventing overflowing water and resulting damage, and were not allowed until the 2006 code (pressure from the 'industry' caused this to be allowed) ... they are now allowed - but only if installed in accordance with the underlined part.
That one is not, neither have any of the others I've seen.
Old 09-27-2007, 09:05 PM
Technically, the switch is installed in the top side (or at least the wires enter through the top) of the primary drain and it would be lower than the rim of the pan (assuming it (the pan) is at the same level as the secondary drain port).
But since I was not able to get a name or model number, I was hoping someone might have a web link or be familiar with this particular switch.
Allen, Texas 75002
Old 09-27-2007, 09:29 PM
Quote:
Yes, but the way the code reads is "A water level detection device conforming to UL 508 shall be provided that will shut off the equipment served in the event that the primary drain is blocked. The device shall be installed ...
That entire 'tee' *is* "the device", at least, that entire 'tee' is the UL listed device, if you take the guts out or modify it in any way, you take away the UL listing.
Thus, to me, "the device" is the "UL listed device", in this case, the 'tee'.
Old 09-28-2007, 06:06 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
It's an SMD Research SS1Low Voltage Condensate Overflow Shut-off Switch.
Link Photo
Link instructions
  #6 (permalink)
Old 09-28-2007, 07:41 AM
Michael Thomas's Avatar
Instructions are here:
http://www.smdresearch.com/index.shtml?products/SafeTSwitch/safetswitchss1.shtml~mainFrame
Here's the catch:
  #7 (permalink)
Old 09-28-2007, 10:46 AM
Thanks, Michael.
Good Info.
Allen, Texas 75002
  #8 (permalink)
Old 07-09-2008, 04:46 PM
Brandon Whitmore Brandon Whitmore is offline
Jerry, I am trying to track down that code requirement now-- you wouldn't happen to know it off the top of your head would you?
Also, what program do you use where you can pull up codes so quickly, copy, and paste them? Also, with that program you are using, are you allowed to copy and past those codes and/ or diagrams directly to a report?
Thanks,
  #9 (permalink)
Old 07-09-2008, 05:08 PM
Quote:
From the IRC.
G2427.7.7 (503.7.7) Clearances.
Minimum clearances
from single-wall metal pipe to combustible material shall be
in accordance with Table G2427.7.7. The clearance from
single-wall metal pipe to combustible material shall be permitted
to be reduced where the combustible material is protected
as specified for vent connectors in Table G2409.2.
Table G2427.7.7
Listed appliances with draft hoods and appliances listed for use with Type B gas vents - MINIMUM DISTANCE FROM COMBUSTIBLE MATERIAL - Single-wall metal pipe - 6 inches
The clearances for the draft hood will be the same as single wall vent, check the installation instructions.
I have the complete set of ICC codes (and others) on my computer.
I always have done it.
While it is "copyrighted material", copyrighted material is allowed to be copied in limited context for "training and education" (as explained to be by several attorneys who dealt with copyright issues). 'Limited context' would be such as copying one page of a code, not the entire code, and using that for 'teaching purposes', or, copying one section from the computer program, when used for 'teaching purposes'. After all, isn't the reason we reference code it 'for teaching purposes'?
Besides, for each state which adopts a code, that information is "public domain" information, which is why the Florida codes are on the Florida and ICC web site, and I believe the ICC codes are on the ICC web site, you can only print one page at a time (if I recall correctly) - for the reason I gave ... it is public domain and for teaching.
Now, if you want "convenience", you have to *pay money* for the printed code books and / or CDs. Believe me, it is worth the money for the convenience.
  #10 (permalink)
Jerry
"located at a point higher than the primary drain line connection and below the overflow rim of such pan."
Are we talking about the internal pan that drains the water to the primary drain line?
OK, What exactly does that mean.
Higher than the primary drain line (always above the rim of the pan)
But below the overflow rim of such pan (how can you have both unless I am not understanding it right.
The primary drain line is always above the rim of the pan. (Unless it is the internal pan)
Ted Menelly
"Castle"
Home Inspection Services
  #11 (permalink)
Old 07-09-2008, 05:12 PM
Quote:
Originally Posted by Ted Menelly View Post
Jerry
Yes.
The primary condensate drain line connects to the primary condensate pan lower than the overflow rim of the pan.
It has to, because the secondary condensate drain line is higher than the primary condensate drain line, and the secondary is intended to allow water filling the pan when the primary condensate line is blocked to overflow into the secondary drain line - without overflowing the rim of the primary condensate pan (otherwise, the secondary condensate drain line would be useless - right?).
  #12 (permalink)
Matthew Barnicle Matthew Barnicle is offline
Jerry, curious why you think they are worthless at preventing overflowing water and damage. If it works properly, and your argument may be that they don't work properly, then it will shut off the condensing unit preventing the pan from overflowing, yes?
  #13 (permalink)
Old 07-09-2008, 05:15 PM
Thanks Jerry
  #14 (permalink)
Old 07-09-2008, 05:22 PM
Ok Jerry
When were talking pans, most of the time we a referring the the lower overflow pan. Just got a little lost there for a moment.
And yes I have seen those switches before installed just like that. I guess to find out if they work we have to go beyond the scope of our inspection and block the drain line and see if the float switch shuts the unit off.
Na, ain't doin it.
Ted Menelly
"Castle"
  #15 (permalink)
Old 07-09-2008, 07:35 PM
Quote:
Matthew,
You lost me on what is worthless.
Guessing you are referring to cut off switches.
Yeah, they don't always work.
Maybe.
If you are talking about the large auxiliary pan, yes, that should keep the pan from overflowing as those pans are typically large enough to catch all the water.
If you are talking about the small primary condensate pan, when the ice on the coil melts (from shutting the system down), no, that water will over flow all over.
Many people (HVAC people) tend to *not think about* iced up coils and what happens to all that water when the ice melts. They assume that the coil is not clogged and dirty, only the condensate line is clogged, so shutting the system off does not produce much water - they think. If you have a full primary condensate pan and shut the unit off, the water being held up on the coil by the fan will run down and overflow the pan anyway.
  #16 (permalink)
Old 07-09-2008, 08:37 PM
Rick Hurst's Avatar
Rick Hurst Rick Hurst is online now
Ted,
Here is an example of a failed shut-off switch. The pan was full of water at this unit and the equipment was still running cranking out the condensation.
As you can tell from the pan, it wouldn't be long till the ceiling below is ruint.
If its electrical you can count on it, it will fail someday.
  #17 (permalink)
Old 07-09-2008, 10:42 PM
Rick
I just looked at that picture for about 3 seconds. I hope you went to your truck and brought your shotgun back in and blew that damn thing out of it misery for your client. What a sorry site the rest of the unit must have been.
Ted Menelly
"Castle"
  #18 (permalink)
Old 07-09-2008, 10:57 PM
Rick Hurst's Avatar
Yeah, after consulting with the owner and other family members we all decided after a prayer that we'd pull the plug on this thing. It had fought a good battle but it was time to say our goodbyes.
Its gone to little evaporator coil heaven.
  #19 (permalink)
Old 07-11-2008, 08:41 AM
Eric Shuman Eric Shuman is offline
Personally (even though allowed by code), I do not trust the float switches as the only means of preventing water overflow in the auxiliary pan. I have tested way too many that did not cut off the unit. As said before "belt and suspenders". When I see a float cut-off switch only and no drain line on the pan I let the client know that it would be better to have a drain line on the pan instead of, or in addition to the float switch.
I told a client as much last week. He had his buddy who is an HVAC guy come out to also inspect the mechanical stuff and he told him the very same thing as soon as he went up in the attic and looked at the unit.
Better safe than sorry IMO. I gotta wonder why the code allows the float switch only approach on the pan. Have the people who wrote this portion of the code never field tested these things?
Eric