oil with gas
Interconnection is allowed per NFPA 211 as long as you meet several criteria:
-There are primary safety controls on both appliances
-There is sufficient draft available for the sale operation of both appliances
-All appliances are located in the same room
In short, it has to work.
Gas combustion produces hydrochloric acid while oil produces sulfuric acid. Both product traces of other acides. Acids are not considered combustible but are corrosive. In addition, the higher the sulfuric acid concentration, the higher the dewpoint. This means burning lower grade #2 oil results in more condensation of acids. Both fuels will cause corrosion. I'd worry more about the liner, vent connectors, makeup air, etc. than interconnection.
John was correct: solid fuel cannot common vent with anything else including other solid fuel appliances.