You are currently viewing InspectionNews as a guest which gives you limited access to view most discussions but not pictures. There are over 4,500 inspectors who have already joined. By joining InspectionNews you will be able to see the pictures, have access to post topics, communicate privately with other members, respond to polls, upload content and access many other special features. Registration is fast and simple so please, join InspectionNews today!
01-10-2008, 05:11 PM
mis matched condenser & handler
Air handler was a 3.5 ton and the condenser 4 ton - same manufacturer/ seer etc/ same year 99. What are the negatives to this and what would be a good recommendation. I have been told it will shorten the life of the unit but i do not understand the reasoning etc.
Thanks!
Jerome
01-10-2008, 05:34 PM
Re: mis matched condenser & handler
Very common match (or mis-match.)
The theory is the larger evaporator coil will boost the EER performance. No biggy in my opinion.
It will not have any appreciable negative effect to my knowledge.
If you want to get real industrious, call the manufacturer with the model numbers and ask.
Some times more than one coil was specified as an acceptable match.
Mr. Inspector.net, Inc.
Allen, Texas 75002
01-10-2008, 05:39 PM
Jim,
It is the other way around. The condenser is actually larger than the handler/coil.
01-10-2008, 05:54 PM
My bad. That might still be an appropriate installation depending on the design as specified by the manufacturer.
A smaller coil will tend to lower the evaporator coil temperature and remove more moisture.
So if you are in an area with a high humidity and low sensible load, this might make sense.
Bottom line, I would not call it a bad installation if it was working properly with no obvious problems just because of an apparent mis-match.
The biggest concern I would look for is coil icing.
Allen, Texas 75002
01-11-2008, 04:35 AM
I have been told by HVAC guys that you can upsize the evaporator by 1/2 ton, but can not down size it at all.
Integrity Inspection Service, LLC
www.irsindy.com
(317) 345-1828
01-11-2008, 05:58 AM
That's also what I've been told, which is probably why Jim stated "The biggest concern I would look for is coil icing."
If the condenser can create more cooling capacity than the evaporator can handle, then icing up would be a distinct and very good possibility (I would think, and Jim confirmed it). Don't know what else it could cause, though.
01-11-2008, 06:21 AM
Jim you are correct. you can do this but must be a proper match by the manufact or warranty will be voided.
01-11-2008, 06:41 AM
Thanks!
Jerome
Call the manufacturer today and ask to speak with the technical desk and they will tell real quick what you need to know. Don't rely on hearsay, get it from the company.
01-11-2008, 07:22 AM
Jerome,
There are evaporator coils that can be used for two different tonnage units. If you go to this web site
Evaporator Coils (Cased) and then scroll down you will see what I am talking about.
As an example, go down to CAPF3642C6 and you will see that it is rated for 3 to 3.5 tons. Now click on the model number and go to the next page. Goodman CAPF3642C6 - Buy Online This explains how the orifice is changed depending on what tonnage you need.
Part of the problem is reading the model number and trying to decide what the rating of the coil is. Every manufacturer does it differently.
I agree with what Jim has said. He knows what he is talking about. If you are in doubt about matched units, give the manufacturer a call with the model numbers from the condenser and evaporator and see what they say.
In my reports I say something like this: I do not have the ability to determine if you have matched units for capacity or SEERS. If this is an area of concern to you, please contact the manufacturer or an HVAC contractor for additional information.
Jeff Euriech
Peoria Arizona
01-12-2008, 06:50 AM
Thanks,
I called a local dealer and the models do not match according to the manufact. recommendations, but they may have changed the coils, etc. Anyway, i explained the scenarios to the buyer and all appears to fine at this point. Hell probably replace the whole system since it is nearly 10 years old.
01-12-2008, 04:52 PM
One other thing to remember about coil ratings, consider the airflow.
The btu or tonnage rating is "x" at "y" cubic feet per minute.
If you decrease or increase the speed of the blower or use a different air handler with the coil, the effective tonnage of the coil is affected.
One more reason sizing, seer ratings and the like is outside the realm of most inspectors, including me.
I might be able to figure it, but I don't, I just look for defects or problems in operation.
I don't calculated gas line size or drain line sizes either.
Allen, Texas 75002
| Thread Tools |
Search this Thread |
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
| Lightning rods on condenser units |
william siegel |
2 |
11-20-2007 04:32 PM |
| air handler in crawlspace |
wes owens |
4 |
06-19-2007 07:54 AM |
| Size of condenser |
James Bohac |
3 |
05-07-2007 07:01 PM |
| Air handler plenum |
william siegel |
8 |
04-21-2007 12:33 PM |
| Fireplace Had It's Own Air Handler Unit |
Nick Ostrowski |
Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection |
6 |
04-03-2007 12:56 PM |