Old 02-25-2008, 08:25 PM
allen elliott allen elliott is offline
Gas furnace
Any Ideas on what caused the soot around the vent. The picture was taken from the bottom side of the flue. It is an upflow furnace located inside an interior closet. It is fueled by propane. Thanks for the input.
Home inspection
Old 02-25-2008, 08:53 PM
Jim Luttrall Jim Luttrall is online now
Re: Gas furnace
Sorry, can't tell much from your picture, got any more? Bigger?
Soot is usually (if not always) caused by incomplete combustion.
Was there plenty of combustion and makeup air?
Did any other appliances or the return air of the furnace itself upset the apple cart with all the doors to the equipment closed?
Is the flue open and sized correctly?
Mr. Inspector.net, Inc.
Allen, Texas 75002
Old 02-25-2008, 09:08 PM
Re: Gas furnace
I am leaning toward the vent. It did not meet the 2-3-10 rule. It was very short and next to a wall on the roof.
Old 02-26-2008, 02:41 PM
Re: Gas furnace
Quote:
"Vents" do not have to meet that rule.
By the way, it is also not 2-3-10, it is 3-2-10 for chimneys.
Old 02-26-2008, 02:53 PM
Steve Lowery Steve Lowery is online now
Re: Gas furnace
What does the 3 refer to?
  #6 (permalink)
Old 02-26-2008, 03:00 PM
Re: Gas furnace
For chimneys:
3 feet high minimum (on sloped roofs you measure the height on the high side of the slope).
2 feet minimum height above any part of any structure within 10 feet.
Home inspection
Similar Threads
Dayton furnace age? Paul Kondzich Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 3 02-05-2008 05:32 PM
Furnace Age Brian Connelly Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 2 07-29-2007 06:01 AM
condensing furnace Bruce Johnson Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection 2 06-28-2007 08:01 PM
Furnace Age David Banks Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 7 05-21-2007 05:58 PM
Furnace vent Jeff Eastman Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 3 04-14-2007 08:28 PM
vB.Sponsors
Ad Management by RedTyger