02-26-2008, 07:42 AM
direct vent?
This indoor air handler is located in a hall closet. I did not notice any combustion air supply, but 2 PVC vents were present. I am assuming that one of them is for supply air, and that this is a direct vent system. Any thoughts?
Ron Bishop
Shasta Lake, Ca.
02-26-2008, 08:05 AM
Re: direct vent?
Ron, were you able to locate the two pipes on the outside of the building? If so you can turn the unit on to see if exhaust comes out of one of the pipes. Anytime they put a unit in a closet it needs exterior combustion air for the heat side. Some municipalities will let it go if the closet has a full louvered door. By the way you say it's an air handler, so is it only providing cooling and heat is supplied by a boiler?
The other issue I see from the photo is that the 90's are DWV fittings. Ok for combustion but not generally accepted for venting. Are you sure it's not poor plumbing venting?
Good luck, Markus
Markus Keller
02-26-2008, 08:22 AM
Re: direct vent?
Excuse me...this is a split system, with the AC unit outsde.
Ron Bishop
Shasta Lake, Ca.
02-26-2008, 08:31 AM
Re: direct vent?
I think Markus was referring to the fact that you didn't mention a furnace. There is a gas furnace there, right? Not just an air handler.
02-26-2008, 08:34 AM
Re: direct vent?
Correct, John
Markus Keller
02-26-2008, 08:36 AM
Re: direct vent?
A furnace is present.
Ron Bishop
Shasta Lake, Ca.
| Thread Tools |
Search this Thread |
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
| Combustion Air venting for Direct Vent FPs |
Clay White |
Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection |
4 |
10-17-2007 04:23 PM |
| Direct vent location |
Clay E White |
4 |
09-24-2007 07:01 AM |
| Gas fireplace direct vent location |
Jon mackay |
14 |
07-11-2007 07:16 PM |
| Gray PVC for direct vent furnace |
Jon mackay |
0 |
06-08-2007 05:52 AM |
| LP tank near direct vent |
Frank Bombardiere |
1 |
05-22-2007 07:11 PM |
Ad Management by
RedTyger