Old 07-02-2008, 10:06 AM
Nick Ostrowski Nick Ostrowski is offline
Furnace & Water Heater in Closet in Bedroom Closet
Here's the setup I saw in a condo this morning. The 2nd floor bedroom closet has another utility closet attached to it that houses a mid-efficient gas fired forced air furnace and a mid-efficient gas fired water heater. Both units have open combustion chambers and vent to the exterior via single-wall mated to type B flue pipe. There are louvered doors on the bedroom closet and the utility closet to draw combustion make-up air. The return air vent in the bedroom is only a few feet from the bedroom and utility closet doors so the return vent is not at least 10' away from the furnace and water heater.
Is it possible that the utility closet within a bedroom closet is a loophole that allows this type of setup? I told my client that normally only direct vent furnace and water heaters would be allowable in a bedroom closet but I'm not sure what type of wrinkle the closet-within-a-closet setup creates. To me, it is still wrong.
Opinions?
Home inspection
Old 07-02-2008, 10:21 AM
Jerry McCarthy's Avatar
Re: Furnace & Water Heater in Closet in Bedroom Closet
Nick
I know you're aware you have caught a gross violation of the IRC's M1701.4 - Prohibited Sources under the Chapter 17 - Combustion Air. The CAR location is also not approved as you have discovered. If you want chapter and verse perhaps EC Jerry will provide, but I’m sure you have a copy of the 2006 IRC or even earlier.
Construction Consultant
Old 07-02-2008, 10:39 AM
Jim Robinson's Avatar
Jim Robinson Jim Robinson is offline
Condo's aren't covered by the IRC are they? I'm sure it's still wrong, but I think you're governed by a different set of rules.
Old 07-02-2008, 12:15 PM
OK Jim, you win:
From the International Fuel Gas Code:
SECTION 303 (IFGC) APPLIANCE LOCATION:
303.1 General. Appliances shall be located as required by this section, specific requirements elsewhere in this code and the conditions of the equipment and appliance listing.
303.2 Hazardous locations. Appliances shall not be located in a hazardous location unless listed and approved for the specific installation.
303.3 Prohibited locations. Appliances shall not be located in, or obtain combustion air from, any of the following rooms or spaces:
1. Sleeping rooms.
2. Bathrooms.
3. Toilet rooms.
4. Storage closets.
5. Surgical rooms.
Exceptions:
1. Direct-vent appliances that obtain all combustion air directly from the outdoors.
2. Vented room heaters, wall furnaces, vented decorative appliances and decorative appliances for installation In vented solid fuel-burning fireplaces provided that the room meets the required volume criteria of Section 304.5.
3. A single-wall-mounted unvented room heater equipped with an oxygen depletion safety shutoff system and installed in a bathroom, provided that the input rating does not exceed 6,000 Btu/h (1.76kW) and the bathroom meets the required volume criteria of Section 304.5.
4. A single-wall-mounted unvented room heater equipped with an oxygen depletion safety shut off system and installed in a bedroom, provided that the input rating does not exceed 10,000 Btu and the bedroom meets the required volume criteria of Section 304.5.
5. Appliances installed in an enclosure in which all combustion air is taken from the outdoors in accordance with Section304.6.Access to such enclosure shall be through a solid weather-stripped door, equipped with an approved self-closing device.
From the 2006 Uniform Mechanical Code:
2006 UMC - 904.0 Central Heating Boilers and Furnaces.
904.1 Location: Central heating furnace and low-pressure boiler installations in bedrooms or bathrooms shall comply with one of the following:
(1) Central heating furnaces and low-pressure boilers may be installed in a closet located in the bedroom or bathroom, provided the closet is equipped with a listed, gasketed door assembly and a listed, self-closing device. The self-closing door assembly shall meet the requirements of section 904.1.1. The door assembly shall be installed with a threshold and bottom door seal and shall meet the requirements of section 904.1.2. All combustion air for such installations shall be obtained from the outdoors. The closet shall be for the exclusive use of the central heating furnace or low-pressure boiler.
(2) Central heating furnaces and low-pressure boilers shall be of the direct-vent type.
904.1.1 Self-Closing Doors. Self-closing doors shall swing easily and freely and shall be equipped with a self-closing device to cause the door to close and latch each time it is opened. The closing mechanism shall not have a hold-open feature. [NFPA 80: 2-1.4.1]
904.1.2 Gasketing: Gasketing on gasket doors or frames shall be furnished only in accordance with the published listings of the door, frame, or gasketing material manufacturer.
Exception: Where acceptable to the Authority Having Jurisdiction, gasketing of noncombustible
or limited-combustible material (see NFPA 220, Standard on Types of Building Construction) shall
be permitted to be applied to the frame, provided closing and latching of the door are not inhibited. [NFPA 80: 2-4.8]
Old 07-02-2008, 12:17 PM
John Arnold John Arnold is offline
Nick - Aside from the question of where the combustion air is coming from, unless the bedroom door itself is vented, or the bedroom is extremely large, it seems unlikely you'd have 50 cubic feet of space per 1,000 BTU.
  #6 (permalink)
Old 07-02-2008, 12:41 PM
The bedroom was wide open to the downstairs with a half wall around the stairwell and no door. Essentially, the upstairs bedroom was a loft so there was nothing to restrict the air flow into the room. Here's a pic I took in the bedroom of the half wall as it had no safety railing around it in the area of the stairs leading to the rear deck (and no handrail on the steps).
  #7 (permalink)
Old 07-02-2008, 05:47 PM
Brandon Whitmore Brandon Whitmore is offline
A handrail may not be required. I am not as versed on building codes, but for the '06 IRC no handrail is required if there is less than 4 risers.
  #8 (permalink)
Old 07-02-2008, 05:57 PM
You need a rail beside the stairs where it looks over the staiwell. You cannot have a knee high or less wall to protect one from falling down the open stairwell.
Ted
  #9 (permalink)
Old 07-02-2008, 06:29 PM
Not if its less than 30 inches in vertical height above the floor Ted.
  #10 (permalink)
Old 07-02-2008, 06:34 PM
I am talking about the small platform in front of the door looking over into the stairwell. I would venture it is a 7 or 8 foot drop to the bottom of the stairwell at the left of the platform. If I am correct that to the left of that half wall is the stairwell coming up to the second floor.
  #11 (permalink)
Old 07-02-2008, 06:44 PM
Quote:
The wall must be at least 36" high above the landing, and, be 36" high above the risers, which likely means the wall is the correct height for the floor, but not for any of the stairway risers/treads.
  #12 (permalink)
Old 07-02-2008, 06:57 PM
Thanks Jerry
I was asuming That was the stairwell to the left.
Ted Menelly
Castle Home Inspection Services
Fort Worth, Texas
  #13 (permalink)
Old 07-02-2008, 08:08 PM
36" at flat surface areas for the IRC, and 34"at the sloped guard at the stairs.... correct?
Also, if this falls under the building code (not residential) doesn't it step up to something around 42"................. man I wish we had one set of codes.
By the way--- Oregon Residential Specialty Code (based off of the '06 IRC) modified the stair guard requirement. Instead of a 4 3/8" gap they decided children were bigger-- ours is now 5" I just caught that the other day since I mostly study off of the IRC.
  #14 (permalink)
Old 07-02-2008, 08:15 PM
The building inspector in Neptune Beach Florida use to maintain 42"
Ted
  #15 (permalink)
Old 07-03-2008, 09:47 AM
That's because under the old Standard codes the height of a guardrail was 42". You had to go to an entirely different section to find the 36" height allowed for residences.
That's why I always used to push the 42" height, and if the builder did not know about the other 36" section, I let the 42" height ride. Also, the old codes address the 36" height as "within" the dwelling unit, meaning the balcony outside was still 42" anyway.
  #16 (permalink)
Old 07-03-2008, 01:51 PM
DavidR's Avatar
DavidR DavidR is offline
That installation is a time bomb waiting to go off.
Due to the return duct configuration and how it is connected to the two other rooms I doubt any combustion air is being provided to those appliances.
If there is air being provided there is a good possibility it is coming from the flue of the water heater.
  #17 (permalink)
Old 07-03-2008, 03:19 PM
In Nick's photo of that 3 step stair leading to the exterior I neglected to notice there was a stair well (or some other sort of drop-off) on the left side looking at the door and my comment was on the less than 30 inch height of the 3 step platform on the right side. Egg on face and I'm looking properly ashamed.
David’s comment made me look again and it looks like the gas appliances in the closet are getting plenty of combo air through the open louvered doors and there was something about the bedroom being a loft and open to a large space?
  #18 (permalink)
Old 07-03-2008, 04:55 PM
Quote:
You are correct Jerry. The bedroom next to that utility closet was wide open with not wall or door separating it from the downstairs area. Essentially, the bedroom was an open loft.
  #19 (permalink)
Old 07-03-2008, 07:28 PM
Quote:
Nick,
Regardless of how open the "bedroom" was, and whether or not the "bedroom" was a loft, it was, nonetheless ... a "bedroom", which is a room for sleeping, i.e., it is a "sleeping room".
As such (being a "sleeping room") that room/area is a prohibited source for obtaining combustion air from it.
  #20 (permalink)
