11-17-2009, 02:56 PM #1
Tankless DV Water Heater Gas Connection
I know codes are different for county to county but generally speaking, would a 20 ft flex gas pipe would be allowed for connection of a tankless water heater?
Similar Threads:Last edited by Al Miha; 11-17-2009 at 04:34 PM.
11-17-2009, 03:06 PM #2
Re: Tankless DV Water Heater Gas Connection
11-17-2009, 03:07 PM #3
I have never seen a 20 ft flex gas line, or a thankless water heater.
I have seen a few indifferent ones though.
11-17-2009, 04:07 PM #4
A "thankless water heater"!! I've never see a "thankless" water heater. Then again I've never seen a thankful water heater either.
Bruce Breedlove
www.avaloninspection.com
11-18-2009, 04:39 AM #5
Would need to know the manufacturer of the csst (of course most are close in how much gas they will allow to pass) to determine, also the BTUs of the tankless (normally around 199,000 ) but some are more and some are a little less.
20' will only supply an aprox 175,000 BTU appliance, with gas pressure in ounces.
Is it an elevated gas system with a regulator at the unit, then 3/4 should be fine.
11-18-2009, 05:58 AM #6
You will need to know what size the line is and at what pressure its at and if it is natural or propane to make a determination. Maximum btu rating of the appliance will also need to be found out.
11-18-2009, 07:15 AM #7
Sorry I should have posted that.
Is a 7.4 gpm, 199000 btu that requires a 3/4 natural gas connector.