Results 1 to 13 of 13
Thread: Why is the TPR valve there?
02-27-2015, 11:13 PM #1
maybe the plumber wanted show up.
Do you think this valve will be functional?
02-27-2015, 11:30 PM #2
Re: Why is the TPR valve there?
The stem for that TPR valve should extend into the tank - not into the fitting or coupling I see above the tank top. Also there are too many bends in the drain line.
02-28-2015, 07:33 AM #3
So many things wrong........and still the rest of the inspection to do......
02-28-2015, 08:04 AM #4
02-28-2015, 08:25 AM #5
Yes.
But the report is not turned into a DIY report because the 'how to fix' is not included, just the 'what is wrong'.
... or is this one of those places that "further investigation and repair by licensed plumber" is warranted?
The only time something close to that would be when an engineer is needed TO DESIGN APPROPRIATE REPAIRS ... NOT to "further investigation ... " by ...
The engineer will determine what, if anything, they need to investigate or evaluate, the engineer will then do whatever calculations they feel are necessary to come up with "appropriate repairs", then whatever the engineer comes up with is what needs to be done.
And, yes, the engineer may determine that 'no repairs are necessary', in which case that is STILL the engineer's design for appropriate repairs.
YOU - the HI - DID THE EVALUATION ... pushing the evaluation off onto others is a bad move, as has been demonstrated here on several occasions. Remember a recent one where the HI called out the electrical panel for "further evaluation by electrical contractor' (or similar wording), then the HI kept complaining that the electrical contractor said it was okay and nothing had to be corrected, yet the photos showed all of us the mess that was in that panel? As soon as the HI turns "the evaluation" over to another ... the HI no longer has any say whatsoever in the outcome.
The HI should NEVER turn the evaluation over to another - or the HI should forevermore keep their mouth shut and never mention anything about that evaluation the other person did. The HI lost all right to say anything about the evaluation when they turned it over to another.
02-28-2015, 08:38 AM #6
I can buy into that. It just gets so frustrating when getting the tank right side up is the only thing they got right.
03-06-2015, 09:53 AM #7
03-06-2015, 11:40 AM #8
While I agree in general with Jerry's comment, as a home inspector, I am a generalist and there are times when I find too many problems with some system or component to put into a report without spending an excessive amount of time on a single system. Electrical is one example. On occasion (I do this only rarely), I will make a statement like - "Numerous improper and unsafe electrical conditions were found during this inspection; including (insert several of the most egregious problems here). A licensed and qualified electrical contractor should be hired to evaluate the entire electrical system and make corrections, repairs or upgrades, as needed."
The same can be true of plumbing, heating and roofing (OMG!).
03-07-2015, 11:28 AM #9
According to the installation instructions in the Kenmore Power Miser 8 owners manual:
“For safe operation of the water heater, the relief valve must not be removed from it’s designated opening or plugged.”
“The temperature-pressure relief valve must be installed directly into the fitting of the water heater designated for the relief valve.”
See page 2, https://www.managemylife.com/mmh/lis...M/99020017.pdf
I would comment that the TPR installation is unsafe and recommend repair by a licensed plumber.
03-07-2015, 03:32 PM #10
03-07-2015, 06:03 PM #11
It appears that the installer of the WH did not want to cut into the wall to lower the relief tubing tie in so it could be plumbed to the outlet in the side of the tank intended for the PRV. Even a proper install would at least require 4 or more elbows (frowned upon code calls for a minimum number of 90 degree turns and we don't know what is in the inside of the wall) if the tank could be rotated and still allow for the burner and pilot access plate. Not well thought out installation and PRV sensor could not reach inside the tank as required to do the job designed for....obviously no permit was taken out for this installation. But maybe this jurisdiction does not require a permit...
03-07-2015, 08:01 PM #12
Not arguing with you, as I caught your line that you rarely do that. But.....I can hear that one now. Well your Honor, I put it all on the Electrician's head right there in them words right there.
What do you mean the Electrician missed it?
The Judge, maybe he would not have missed it if you would have written it down! After all, there must have been something you could have specifically written about the numerous unsafe issues. And was this one of them?
PROFESSIONAL CONSULTING AND INSPECTION COMPANY INCLUDING FORENSIC INVESTIGATIONS
http://jeffghooper.com/
03-08-2015, 11:57 AM #13
Good Point JeffG,
I think the statement that I use also includes something to the effect of "... other improper and/or unsafe wiring conditions are likely present" before deferring.
Once again, I am a generalist and feel that noting every single problem/condition when the entire system is in poor shape would either end up with me spending an excessive amount of time on an inspection or neglecting other parts of the home, while still missing some problems (who checks wire size at a splice?).
How about "Well your honor, I was so busy documenting all of the egregious electrical problems that I didn't notice the ancient furnace belching flames..."
I think this also goes along with "last man in". The electrical contractor is the expert and I deferred the entire system to his expertise.
