07-01-2015, 11:27 AM #1
Is insulation required for PEX type piping?
I almost never see hot water distribution pipe (PEX type) insulated. The energy code requires R3?
Is PEX rated R3?
Do you call this out on your reports??
07-01-2015, 01:11 PM #2
Re: Is insulation required for PEX type piping?
R Value of Pex is very similar to cooper.
If you AHJ requires R3 then Pex needs to be insulated as cooper supply would be to meet this requirement.
02-19-2016, 01:17 PM #3
Old post resurrection.
Yes. I call it out. Pex manufacturers recommend it. From a Viega manual....
15.6
Freezing
The flexibility of ViegaPEX Ultra tubing makes it
resistant to damage from freezing, but precautions
to prevent freezing should be taken when low
temperatures might be encountered.
Insulating each PEX tube individually or as a group is
not generally necessary if the PEX tubing is installed
within the insulation envelope of the structure, i.e. the
heated area. For example, the tubing may be installed
under the insulation in the attic or within an interior wall
of a heated space.
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
02-19-2016, 01:27 PM #4