08-04-2015, 03:09 PM #1
Water heater expansion device in new construction
Hello!
Looking at the picture, is this installed correctly. Or like the PRV extension, it has to be installed going down hill since it is gravity fed. Thanks, Jim
08-04-2015, 05:19 PM #2
Re: Water heater expansion device in new construction
It is not gravity fed. It operates by pressure, so orientation does not matter.
The reason why a TPRV discharge pipe goes downhill is so water cannot sit in the pipe.
This relief valve should not be isolated from the water heater by a shut off valve.
08-04-2015, 05:35 PM #3
Thanks,
Would you please explain in more detail, "This relief valve should not be isolated from the water heater by a shut off valve."
Jim
08-25-2015, 11:37 AM #4
08-25-2015, 02:22 PM #5
That valve in the photo is not a temperature and pressure (T&P) relief valve, it is a pressure only relief valve. The reason for that valve is thermal expansion when the water heater is on and heating the water, so, as Mark said, the pressure relief valve should be on the tank side of the shut-off valve (the shut-off valve should not be between the pressure relief valve and the tank).
Having that shut-off valve there will not ... 'SHOULD NOT' is the better wording ... cause any harm to the water heater or anything around it as the T&P relief valve is still installed in the tank - hopefully a proper T&P is properly installed in the tank.
The thermal expansion pressure relief valve is there to keep water from being pushed back into the utility's supply to the house. Nothing else.
08-25-2015, 02:53 PM #6