Results 1 to 27 of 27
02-08-2008, 01:45 PM #1
Protection from car hitting water heater
Is there code that requires a balun or some kind of protection to prevent a car from striking a water heater, especially a gas water heater?
On a recent inspection, the gas water heater was at the front part of the garage and had nor protection to prevent a car from hitting it. I am thinking this is an accident (explosion) waiting to happen.
Thanks!
02-08-2008, 02:25 PM #2
Re: Protection from car hitting water heater
Yes, protection from vehicle damage in a garage is required.
02-08-2008, 02:35 PM #3
Robert,
A bollard is required, but it is to protect the gas piping from vehicle damage. This would be true for any gas piping if it is in a location that it could be hit by a vehicle. This might also mean the furnace or gas meter as well. Unfortunately, I am unable to locate the specific code. Maybe someone else will chime in.
02-08-2008, 02:38 PM #4
02-08-2008, 04:07 PM #5
I meant to say bollard - that is the correct term. A balun is used in video for changing from one type of cable to another. Sorry about the confusion.
02-08-2008, 05:05 PM #6
Found it (I think)
2000 IRC: 1307.3.1
02-08-2008, 05:23 PM #7
Can someone post a picture of a water heater that actually has a bollard in front of it?
I've never seen one. I understand its need but it is something that is not enforced here the any AHJ I know of.
The picture could be a reference for us to show clients.
Thanks in advance.
02-08-2008, 06:45 PM #8
02-08-2008, 07:08 PM #9
Rick,
I will look, but no guarantees. I generally do not take pics of things that are correct.
02-08-2008, 07:17 PM #10
Rick is found this diagram that Jerry M. posted a while back on this thread:
http://www.inspectionnews.net/home_i...er-heater.html
Not a picture of a correct one, but a couple of diagrams and an incorrect installation.
02-08-2008, 07:19 PM #11
Actually, gas piping be damned!
, it is to protect the water heater, and any appliance.
And it does not need a "bollard", just "vehicle protection".
- P2801.4 Prohibited locations.Water heaters shall be located in accordance with Chapter 20.
- M2005.1 General.Water heaters shall be installed in accordance with the manufacturer’s installation instructions and the requirements of this code.Water heaters installed in an attic shall conform to the requirements of Section M1305.1.3. Gas-fired water heaters shall conform to the requirements in Chapter 24. Domestic electric water heaters shall conform to UL 174 or UL 1453. Commercial electric water heaters shall conform to UL 1453. Oiled-fired water heaters shall conform to UL 732.
- M2005.3 Electric water heaters. Electric water heaters shall
also be installed in accordance with the applicable provisions of Chapters 33 through 42.
"manufacturer’s installation instructions" will tell you to protect it from vehicle damage if installed in a garage.
02-08-2008, 08:23 PM #12
My area has them now and pretty much has for the last 10 years or so. On construction prior to that they were pretty scarce.
In a cont. ed class once I was taught that they are supposed to also be in front of electric meters. Enforcement on that one is totally unheard of around here.
02-08-2008, 08:30 PM #13
02-08-2008, 08:44 PM #14
From Jerry M's Post
Bollard Protection today.
02-08-2008, 09:01 PM #15
Rick,
Here you go. The last one is the best of the lot. Actually, pretty good. I will email it too.
02-08-2008, 09:27 PM #16
Gunnar,
The 3rd photo is not filled with concrete. That pipe will just bend like a pretzel.
02-08-2008, 09:37 PM #17
Gunnar,
Thanks for posting those.
02-08-2008, 10:53 PM #18
Not if you tap it very lightly with a "SmartCar".
Rick,
You are welcome.
02-08-2008, 11:28 PM #19
To carry this a little further, how about "water heaters" used only as water storage tanks, the heating being done with a tankless coil in a boiler? Do these need vehicle protection? Also, do they need TPR's?
02-09-2008, 01:45 PM #20
Chris,
- P2803.1 Relief valves required. Appliances and equipment used for heating water or storing hot water shall be protected by:
- - 1. A separate pressure-relief valve and a separate temperature-relief valve; or
- - 2. A combination pressure- and temperature-relief valve.
02-09-2008, 08:44 PM #21
Ok... I'll add a picture also.
I took it because it is unusual to see one.
I started to wonder about the redneck ingenuity of using duct tape for everything, but, it was pretty strong tape, the thing wouldn't budge when I kicked it.
www.Home2Spec.com
02-10-2008, 10:09 AM #22
Hi Gunner
I see a code violation on every one of your photos. It seems like when we are demonstrating a particular defect there's always another one somewhere in the background. That's why inspectors who include defect photos in their reports should be extra careful in what they are calling, or in particular, not calling out.
PS: I'd bet you caught them all.
02-10-2008, 11:09 AM #23
02-10-2008, 12:04 PM #24
If a bollard is too much trouble to install, you can always recommend a red Ferrari. It does a great job of stopping a vehicle.
What amazes me more than anything about this picture is those Arkansas license plates.
02-10-2008, 02:33 PM #25
04-08-2008, 07:05 PM #26
This came up today on an inspection, and right there in the manuf. installation manual in "black and white" it states that a WH should be protected against damages from a moving vehicle.
04-09-2008, 06:58 PM #27
Here is a picture of one I inspected today.
Yes, I know the black foam insulation is in contact with the flue.
