LP gas water heater vent iissue
LP gas water heater in exterior compartment; 4' and 6' away from windows, 1' away from air condenser, 4' below soffit vent, dryer vent at lower right with crawl space vents to the right further. I guesting not correct; should the vent be extended above the roof line. Thanks, Mark
Similar Threads:
-
06-03-2019, 02:11 PM #2
Re: LP gas water heater vent iissue
Unless the listing, labeling, and installation instructions say otherwise, my recollection is that the type B gas vent needs to terminate a minimum of 2 feet above a wall/obstruction within 8 feet.
-
06-03-2019, 05:17 PM #3
Re: LP gas water heater vent iissue
Is there actually a natural draft appliance in that enclosure?
Is it rated for exterior installation when installed in an approved cabinet?
Is the B-vent extending 5 feet above the draft hood?
And yes, the 2/10 rule applies due to the adjacent wall being within the 8 feet measurement.
Dom.
-
06-03-2019, 06:15 PM #4
Re: LP gas water heater vent iissue
Also, did you notice the concrete blocks under the condenser unit slab?
They are facing the wrong way and have no rated capacity with the cells horizontally like that - the face shells, webs, and ends are supposed to be vertical.
Fortunately, the risk of block failure is small under that condenser unit and its pad, but the risk is still there - I would include it in the report so you are advising your client that it needs to be corrected (not that it will likely ever be corrected, but at least you will be able to say "I put that in my report, you DID read the report and see that listed as a 'needs to be done item', right?"
-
06-04-2019, 04:30 AM #5
-
06-05-2019, 11:09 PM #6
-
06-06-2019, 06:10 AM #7
Re: LP gas water heater vent iissue
Just from the first picture you can bet on two things; This house is going to have a very Long Report...And the fee for the inspection was not high enough....but we never know till we pull up on the job, do we. Too bad we can't charge by word and photo count on reports like the newspapers do when they publish their "Obituaries"....
Apollo Home Inspection
St. George UT
-
06-06-2019, 07:07 AM #8
Re: LP gas water heater vent iissue
-
06-19-2019, 09:50 AM #9
Re: LP gas water heater vent iissue
-
06-23-2019, 08:26 AM #10
Re: LP gas water heater vent iissue
For outdoor Aquahuts you can use a Field Controls Star-Kap as prescribed in the attachment if approved by your AHJ.
Enjoy!