Old 07-17-2007, 10:09 AM
cleanouts
Old 07-17-2007, 10:27 AM
Robert Schenck's Avatar
Robert Schenck Robert Schenck is offline
Re: cleanouts
If you're referring to a sinks P-Trap, ... all sinks require them. Now, some of the P-Traps I've seen do have the threaded clean-out cap (on bottom of trap). Whether their required or not is unknown to me. If they have the clean-out cap, .. great, ... if they don't, it's just a matter of uncoupling the P-Trap, removing it and cleaning out all of the gunk and wifes hair !!
Robert
Roberts Home Inspection Service
Old 07-17-2007, 10:32 PM
Martin lehman's Avatar
Martin lehman Martin lehman is offline
Re: cleanouts
No, cleanouts are not required under sinks. Cleanouts are generally required where the drain lines change direction more than 45 degrees.
Were there cleanouts under all the sinks in the home??
Old 07-18-2007, 08:17 AM
Re: cleanouts
I think my post above was a little misleading. I meant to say that all sinks, etc, require P-Traps, ... and not clean-outs.
Robert
Old 07-18-2007, 09:32 AM
brian schmitt brian schmitt is offline
Re: cleanouts
jeff,
cleanouts are required in new construction for sinks.u.p.c. 707.4 each horizontal drainage pipe shall be provided with a cleanout at its upper terminal and each run of piping. exc.(1) cleanouts may be admitted on a horizontal draain line less than 5 feet in length unless such line is serving sinks or urinals.
  #6 (permalink)
Old 07-19-2007, 10:32 PM
Re: cleanouts
I must correct myself, Brian you are right. However there is also another exception to the rule. If a REMOVABLE trap is installed there is no cleanout needed.
This is the norm out here. I rarely see a trap with a cleanout.