Old 11-16-2007, 10:04 AM
Matthew Barnicle Matthew Barnicle is offline
jacuzzi tub motor bonding lug
When is the bonding lug on the jacuzzi bathtub motor required to be used/utilized? Examples?
Old 11-16-2007, 10:24 AM
paul hardy paul hardy is online now
Re: jacuzzi tub motor bonding lug
the bonding lug is used to connect any metal plumbing system located under the tub or any metal parts in contact with the circulating water together.
Old 11-16-2007, 11:42 AM
"the bonding lug is used to connect any metal plumbing system located under the tub or any metal parts in contact with the circulating water together."
Is this required? Wouldn't the grounding pin on the attached cord bond the motor to the plumbing system since the supply pipes are bonded to the electrical system?
Old 11-16-2007, 02:30 PM
fritzkelly fritzkelly is offline
When this has come up in the past, most everybody (even Jerry I think)agreed that the bond was not needed if the piping to the jets was plastic. I have never seen a jetted tub with metal piping so I don't call it out except in cases where the bonding wire is there but is not connected. I figure if the electrician went to the trouble to run the wire he should connect it.
Old 11-16-2007, 05:08 PM
Gunnar Alquist's Avatar
I see tub motors with bonding clamps and without. I figure that if the manufacturer went to the expense of putting the clamp on the motor, then they intended it to be used. If I don't see a clamp, then I don't mention it.
The apostrophe troll.
  #6 (permalink)
Old 11-16-2007, 07:11 PM
From the NEC.
(2002)
- 680.74 Bonding.
- - All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid. Metal parts of listed equipment incorporating an approved system of double insulation and providing a means for grounding internal nonaccessible, non–current-carrying metal parts shall not be bonded.
(2005)
- 680.74 Bonding.
- - All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid.
In 2005 it changed quite a bit. For 2005 - *IF* the piping is *not* "metal", and there are no grounded metal parts in contact with the circulating water (other than the pump motor itself), nothing needs to be bonded.
(2008)
- 680.74 Bonding.
- - All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a solid copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG. The bonding jumper shall be connected to the terminal on the circulating pump motor that is intended for this purpose. The bonding jumper shall not be required to be connected to a double insulated circulating pump motor. The 8 AWG or larger solid copper bonding jumper shall be required for equipotential bonding in the area of the hydromassage bathtub and shall not be required to be extended or attached to any remote panelboard, service equipment, or any electrode.
Similar Threads
Hydro-therapy Tub Motor ? Rick Hurst Built-In Appliances and Systems: Home Inspection and Commercial Inspection 9 10-18-2007 05:38 PM
Whirlpool Tub Motor Joe Nernberg Plumbing System: Home Inspection and Commercial Inspection 1 06-29-2007 05:27 PM
Whirlpool Tub Motor Joe Nernberg Plumbing System: Home Inspection and Commercial Inspection 3 06-29-2007 08:59 AM
Bonding Michael Vasquez Electrical Systems: Home Inspection and Commercial Inspection 2 04-23-2007 04:47 PM
Bonding of raceway Dave Hahn Electrical Systems: Home Inspection and Commercial Inspection 12 04-09-2007 06:57 PM
vB.Sponsors
Ad Management by RedTyger