Old 11-26-2007, 03:28 PM
Greg Jenkins Greg Jenkins is offline
Elbows in T & P drain pipe
Can anyone tell me if there is a limit to how many elbows can be in a hot water tank T&P drain pipe. I seem to recall that there is definitely a limit but I can not find the answer.
Greg
Greg Jenkins
Old 11-26-2007, 05:09 PM
Re: Elbows in T & P drain pipe
4 elbows maximum.
30 feet long maximum, all down hill.
It's right on the tag. (It's also on the Watts website where the T&P valves are, at least it was years ago.)
Old 11-26-2007, 05:28 PM
Thanks Jerry.
Is that 4 - 90's or any elbow?
Greg Jenkins
Old 11-26-2007, 06:11 PM
Quote:
It says 'four elbows', does not specify whether 90 or 45 - either would disrupt the flow to some extent and create a bit of back pressure, back pressure is one thing they do not want - get the water out and get it out fast.
Old 11-26-2007, 06:25 PM
Ok, we'll go with four of any elbows for now but I know I have read specific documentation on this subject before I just cann't seem to locate it. If any one else knows the specifics, please chime in. On this mornings inspection the pipe had three 90's and a 45 then they shot it straight thru the wall to the exterior but did not point it toward the ground. It also was not protected from freezing (but that's another issue).
Greg Jenkins
  #6 (permalink)
Old 11-26-2007, 07:26 PM
Jerry McCarthy's Avatar
Jerry
4 elbows: you got a code section # for that or is it only mafg inst. instructions?
Construction Consultant
  #7 (permalink)
Old 11-26-2007, 07:53 PM
Quote:
Originally Posted by Jerry McCarthy View Post
Jerry
Manufacturer's installation instructions, but ... since Greg's last post above I've off and on been trying to find it on the Watt's web site, however, it seems they are changed all the requirements now that the codes say that the T&P relief valve discharge line must terminate in the same room as the water heater is.
Attached is an older one, but I can no longer find that valve on Watts' web site.
Thus, on houses 'before' the newer codes (since 2000-2003) came into affect, the 30 feet and not more than four elbows was the rule (Watts' rule).
However, on newer homes, the 'shall terminate in the same room as the water heater is' is the rule (code).
  #8 (permalink)
Old 11-26-2007, 08:59 PM
Michael Thomas's Avatar
Here ya' go:
Watts Water Safety and Flow Control Products - balancing valve, ball valve, butterfly valve, check valve, relief valve, temperature gauge
  #9 (permalink)
Old 11-27-2007, 07:02 AM
I must of read that page 10 times last night and missed that 30' / 4 elbows part in there every time.
Glad to see it is still in there.
  #10 (permalink)
Old 11-27-2007, 09:33 AM
Jeff Euriech Jeff Euriech is offline
Interesting.... Under "REINSPECTION OF T&P RELIEF VALVES" it says you should pull the TPR valve once every three years and inspect it. I never knew that. Learn something new everyday.
Jeff Euriech
Peoria Arizona
  #11 (permalink)
Old 11-27-2007, 10:27 AM
Gunnar Alquist's Avatar
Jeff,
Inspect every 3 years? Yeah, that's going to happen.
The apostrophe troll.
  #12 (permalink)
Old 12-06-2007, 10:54 PM
I just remember it by doing it after every 36th time I test all of the my GFI's.... Is there an easier way?
  #13 (permalink)
Old 12-06-2007, 11:30 PM
charles buell charles buell is offline
Hi all,
first post and all but thought I would jump into the fray on this one. The 2003 IRC doesn't say anything about the drain "having" to terminate in the same room and the 2006 is no different. I know in my neck of the woods I rarely see it terminate indoors unless it is very difficult to get it to the outside.
From the IRC: "P2803.6.1 Requirements of discharge pipe.
The outlet of a pressure relief valve, temperature relief valve or combination thereof, shall not be directly connected to the drainage system. The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building. In areas subject to freezing, the relief valve shall discharge through an air gap into an indirect waste receptor located within a heated space, or by other approved means. The discharge shall be installed in a manner that does not cause personal injury or property damage and that is readily observable by the building occupants. The discharge from a relief valve shall not be trapped. The diameter of the discharge piping shall not be less than the diameter of the relief valve outlet. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches (152 mm) above the floor. The outlet end of the discharge pipe shall not have a valve installed." Perhaps UPC areas say something different?
  #14 (permalink)
Old 12-07-2007, 07:54 AM
Richard Stanley Richard Stanley is offline
2006 IRC
P2803.6.1 Requirements for discharge pipe.
The discharge
piping serving a pressure-relief valve, temperaturerelief
valve or combination valve shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same
room as the water heater.
3. Not be smaller than the diameter of the outlet of the
valve served and shall discharge full size to the air
gap.
4. Serve a single relief device and shall not connect to
piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor
or to the outdoors. Where discharging to the outdoors
in areas subject to freezing, discharge piping
shall be first piped to an indirect waste receptor
through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal
injury or structural damage.
7. Discharge to a termination point that is readily
8. Not be trapped.
9. Be installed to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above
the floor or waste receptor.
11. Not have a threaded connection at the end of the piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section
P2904.5 or materials tested, rated and approved for
such use in accordance with ASME A112.4.1.
  #15 (permalink)
Old 12-07-2007, 09:24 AM
Richard, there is also #5 in the 2006.
  #16 (permalink)
Old 12-07-2007, 10:28 AM
#5 is applicable to the drain pan under the WH.
  #17 (permalink)
Old 12-07-2007, 10:59 AM
Where does it say that? The way I read it, all 13 items apply to the "discharge piping." No?
  #18 (permalink)
Old 12-07-2007, 06:00 PM
Charles,
#5 is referring to where the discharge from the air gap can discharge to.
FIRST do #2, THEN you have to drain that 'somewhere' and #5 tells you where you are allowed to drain that to.
  #19 (permalink)
Old 12-07-2007, 07:16 PM
Jerry, I see the "list" as what can and can not be done---I just don't see any if-then to the list. What you are saying may be what was "intended" by the change from 2003---but it is not what it says. I expect we will be seeing more clarification on this one. Like I said previously, I am not seeing any terminations on the interior of the home unless there is no other way to do it---of course not very many jurisdictions have adopted the 2006IRC in my area----none that I know of.
  #20 (permalink)
Old 12-07-2007, 09:03 PM
Charles,
Maybe it will help if I post it this way:
- 2006 IRC
- - P2803.6.1 Requirements for discharge pipe. (Jerry's note: The following *are* *requirements* for the relief valve discharge pipe.)
- - - The discharge piping serving a pressure-relief valve, temperature relief valve or combination valve shall: (Jerry's note: "Shall" have, i.e., the following are "shall" requirements except where given as options.)
- - - - 1. Not be directly connected to the drainage system. (Jerry's note: The discharge line "shall" not be directly connected to the drainage system - this is a "shall" requirement.)
- - - - 2. Discharge through an air gap located in the same room as the water heater. (Jerry's note: The discharge line "shall" discharge "through an air gap" - that is a "shall", not an option - "located in the same room - that is a "shall", not an option - these are "shall" requirements.)
- - - - 3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap. (Jerry's note: The discharge line "shall" not be smaller than the diameter of the valve outlet - this is a "shall" requirement.)
- - - - 4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment. (Jerry's note: The discharge line "shall not" be connected to any other piping - this is a "shall" requirement in the negative, i.e., "shall not".)
- - - - 5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.(Jerry's note: These are discharge line 'options', i.e., this gives you choices on where the discharging water is allowed to discharge - this is a "shall" requirement with several 'options' to the "shall".)
- - - - 6. Discharge in a manner that does not cause personal injury or structural damage. (Jerry's note: The discharge line "shall" discharge in a manner in which the discharge does not cause personal injury or structural damage - this is a "shall" requirement stating a negative in a positive manner, i.e., you "shall not" discharge to - for example - the interior wall space as that could cause structural damage, or, you "shall not" discharge at a height and location which could discharge directly into the face of a person as this could cause personal injury, i.e., -