Old 07-24-2008, 02:36 PM
Bruce Ramsey's Avatar
Bruce Ramsey Bruce Ramsey is offline
Exposed CSST full length of wall
1 year warranty inspection this morning. It looks like the house was built for an electric dryer but the buyers wanted gas. Someone punched a hole in the laundry room ceiling, ran CSST down the wall, secured the CSST to the cabinet and drywall. When the CSST reached the floor, installed a rigid elbow and shutoff valve, then back to CSST behind the dryer.
Since CSST is so fragile, it seems that there is probably some requirement that it not be exposed on the interior. Did not find anything in Code Check under plumbing that helped. Any pointers?
Bruce Ramsey
Advocate Inspections
www.NCAdvocate.com
Home inspection
Old 07-24-2008, 02:44 PM
John Arnold John Arnold is online now
Re: Exposed CSST full length of wall
I don't think CSST is "that fragile", but it's clearly an amateur job. And, I don't see no drip leg, neither. I would call for a professional to come in and do it right.
Old 07-24-2008, 03:21 PM
While being butt ugly and having several 'questionable' routing practices shown in the photo, I don't see anything in the manufacturer's installation instructions 'prohibiting' "exposed work".
In fact, you can even have "exposed work" on a roof, and that is specifically addressed, so I would suspect that "exposed work" inside would also be allowed.
If the homeowner had it installed, I would just advise them that, when they go to sell, it may well come up, and that if they had the installed come back and fish it down the inside of the wall, the top and bottom could be enclosed, making that future problem not be a future problem.
Old 07-24-2008, 03:28 PM
Nick Ostrowski Nick Ostrowski is offline
John, my Code Check Plumbing book says clothes dryers are an exception for sediment traps on the gas line along with ranges, gas lights, and gas grills.
IRC 2419.4
According to this, it should be OK w/o the drip leg/sediment trap.
Old 07-24-2008, 04:57 PM
Brandon Whitmore Brandon Whitmore is offline
IRC 2419.4
I agree with Nick that it is allowed to be installed without the trap. Under the commentary that Jerry posted a while back, they recommend a sediment trap, but do not require one.
  #6 (permalink)
Old 07-24-2008, 05:00 PM
wayne soper's Avatar
It should however be protected from damage. If that is in an area where large items are stored or moved around a puncture is possible.
  #7 (permalink)
Old 07-24-2008, 08:12 PM
Billy Stephens's Avatar
Billy Stephens Billy Stephens is offline
Surely those Conduit Straps Cannot be Approved for this Application.
Billy J. Stephens HI Service
  #8 (permalink)
Old 07-24-2008, 08:59 PM
Quote:
Actually, they are.
From the 2008 Gastite Design and Installation manual. (underlining is mine)
f) Supporting CSST - Tubing shall be supported in a workmanlike manner with pipe straps, bands or hangers suitable for the size and weight of the tubing, at intervals not to exceed those shown in Table 4-2. A proper support is one which is designed as a pipe hanger, does not damage the tubing during installation, and provides full support. “J” Hooks may not be used as they may damage the CSST. Zip Ties/Cable Ties are not to be used as a primary support but may be used to organize or bundle CSST. See Table 4-5 for supporting CSST in a rooftop application.
That is their only requirement "suitable for the size and weight", I called them years ago and they said sure, EMT straps a okay, although at the time they said they "prefer two hole EMT straps over the one hole EMT straps".
If you have the 2008 manual, look at Fig 4-24 (page 49), you will see what looks like 1 one hole EMT strap and 1 two hole EMT strap securing the ends of the CSST.
  #9 (permalink)
Old 07-24-2008, 09:32 PM
Quote:
Actually, they are.
THANKS.
Similar Threads
CSST through exterior wall? Bruce Ramsey Plumbing System: Home Inspection and Commercial Inspection 4 05-07-2008 09:07 AM
Full Size Van vs. other vehicles Bruce Ramsey Tools and Equipment 41 01-25-2008 09:52 PM
Full moon, April 1 or Halloween? BARRY ADAIR General Chit Chat: Home Inspectors & Commercial Inspectors 2 01-08-2008 07:06 PM
Earth contact homes - exposed foundation wall insulation above grade Shane Pouch Building Envelope: Home Inspection and Commercial Inspection 4 12-07-2007 07:27 AM
Plenum length william siegel Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 8 05-06-2007 01:28 PM
vB.Sponsors
Ad Management by RedTyger