Old 05-06-2008, 05:31 PM
Jerome W. Young Jerome W. Young is offline
a/c condensers bonded to pool equipment
I dont know why they did this. Anyone see a problem?
Old 05-06-2008, 06:39 PM
Re: a/c condensers bonded to pool equipment
If the a/c condenser unit was within 5 feet of the pool water, it would be required.
The problems I see are: air flow clearance issues around the a/c condenser unit, working space issues at the pump and the condenser unit, liquid tight conduit not properly secured and supported (not that I can see that, it's just a 'very high probability of being correct' guess).
Old 05-06-2008, 07:24 PM
James Duffin James Duffin is offline
The bonding is correct as long as it is a nut and bolt connection and not a sheet-metal screw.
Old 05-06-2008, 07:58 PM
Quote:
And, as long as we are getting into the connection in that depth, the paint needs to be removed where the terminal and washer make contact with the side of the condenser unit. Of course, though, now one must be concerned about rusting at that location.
Old 05-06-2008, 08:11 PM
You should know that a bolted connection is required. The sheet-metal screw has very little metal to metal contact so it it no allowed. The paint is not an issue in this application.
  #6 (permalink)
Old 05-07-2008, 06:11 AM
I do know that, but originally we were not discussing 'how the connection was made'.
Paint is not a good conductor, and the paint needs to be removed when that bolted connection is made, because that bolted connection is made, not by contact between the bolt and the inside of the hole (as you said, even a sheet metal screw which cuts into the metal is a poor connection there, much less a bolt through a drilled hole), but is made by compressing the terminal (for the bond wire) to the metal between the terminal and the washer under the bolt head/washer&nut.
Unless you scrape the paint off, all you are doing is clamping terminal-to-paint and bolt/washer-to-paint, using the metal only to hold the paint in place.
That connection is unlike a ground screw in a box or panel enclosure. First, those have metal which is thinker, and their holes are threaded, for use with threaded screws, and the connection between the threaded screw and the metal is the electrical connection, because it is so much better than a sheet metal screw into metal.
If you've even seen one of those connections take a hit, you will notice the scorch arc mark all around the head of the terminal where the arc burned through the paint to make more contact when the threads could not carry the current load.
Those connections are not required to have the paint scraped off, because they are threaded and have what has been deemed 'adequate' metal-to-metal contact at the threaded ground screw itself.
  #7 (permalink)
Old 05-07-2008, 11:43 PM
Matthew Barnicle Matthew Barnicle is offline
If the condensing unit was in any way used to heat the pool, it would be required. Some units have a recirculating pump like for a heat recovery unit for a water heater.
  #8 (permalink)
Old 05-08-2008, 06:07 AM
Quote:
This is true, except ...
I've seen thousands of pool heat pumps and none looked like a regular a/c condenser unit, and ...
If it was a regular a/c condenser unit being used for that use, it would be being used outside of its listing and labeling - all equipment used for swimming pools need to be listed and labeled for that use. Thus, if that were the case, the photo would be doubly bad.
Similar Threads
USED EQUIPMENT SHOULD NEVER BE REUSED! Joe Tedesco Electrical Systems: Home Inspection and Commercial Inspection 7 04-21-2008 05:22 PM
sub panel bonded with neutrals Jerome W. Young Electrical Systems: Home Inspection and Commercial Inspection 5 02-22-2008 05:37 AM
Electrical panel bonded ? Lynn Petrie General Chit Chat: Home Inspectors & Commercial Inspectors 3 09-17-2007 09:38 AM
Pool equipment foundation in need of repair? Rick Hurst Pool and Spa: Home Inspection and Commercial Inspection 3 09-12-2007 12:18 PM
A/C Condensers next to the pool Mike Pearson Pool and Spa: Home Inspection and Commercial Inspection 12 07-23-2007 03:07 PM
vB.Sponsors
Ad Management by RedTyger
