Results 1 to 11 of 11
    Daniel Island, SC.
    Default 2/12 slope for shingles
    Is it possible to have a 2/12 sloped roof shingled? If so, what is the criteria?
    Also what if they used a ice and water underlayment? Would that be acceptable with shingles if they decreased the exposure?
    The house is ocean front.
    Jim
    Default Re: 2/12 slope for shingles
    Quote Originally Posted by JIM MURPHY View Post
    Yes, some manufacturers allow down to a 2/12 slope as I recall. How? According to their installation instructions.
    I believe the underlayment is doubled over what is normally called for.
    Might work and might be acceptable, you would need to check the manufacturer's installation instructions.
    Knoxville, TN
    2/12 is the minimum slope for shingles
    You sure?
    The ones I recall are 2-1/2 in 12 or 3 in 12, as I recall (although it has been a while since I have looked as I have not found shingles on that low of a slope in years.
    Jun 2010
    West Chester PA
    A shingle installation on anything less than 4 / 12 in this area,
    I recommend a roofer review along with repairs to correct deficiencies.
    Snow loads the last couple of winters have been incredible.
    your mileage may vary.....
    Jun 2008
    Chapter 9 - Roof Assemblies
    IRC is the same language too.
    Typically, the manufacturer's installation instructions are going to recommend or require upgraded underlayment, and reference the appropriate ASTM standards.
    I tell clients "In my opinion, in our climate at 2/12 the shingles are a 'decorative roof covering', and it's the underlayment providing the water resistance".
    What about all the shingle nail holes in your nice underlayment?
    Nobody shingles a 2 in 12 in my area, the wild Wet Coast. It would leak. Period.
    A few years back, I saw a 3 in 12 shingled and I called it suspect. The shingle exposure should be reduced an inch or more for 3 in 12. Forget about anything like 2 in 12. That would need torch-on modified bitumen. At least, that is what they do here.
    In my experience, here in Chicago properly self-adhesive WSU is sufficiently self-healing to work successfully under comp shingles installed at any slope allowed by the manufacturer.
    Which is not to say that I think such installations between 2/12 - 4/12 are a Good Idea, but only that 1) I personally have not seen them fail due to water intrusion through the underlayment and 2) I cannot fault them for violating the manufacturer's installation instructions.
    More often, I'm writing them up at HIs or WIs because the underlayment does not even meet the manufacturer's installation requirements or R905.3.3.1 and/or because of flashing or similar details - I should be so lucky as to find WSU!
    Knoxville, TN
    I'm pretty sure. I re-checked and R905.2.2 covers it.
    Oct 2011
    Minneapolis, MN
    Might wind be a concern on a ocean front house with such a low pitch?
