Results 1 to 10 of 10
Thread: Flue clearance
    Baton Rouge, La.
    Default Flue clearance
    Does a water heater flue pipe require the same 3-2-10 rule same as firplaces. For the life of me I cant find my reference.
    Jim
    David Banks's Avatar
    David Banks Guest
    Default Re: Flue clearance
    Do not have code but if closer than 8 feet to wall vent must extend 2 feet above roof.
    Jim, I'm not sure about that. But how close is that flue pipe to the adjacent roof surface? Is that type-B vent or single walled?
    Baton Rouge, La.
    That's single walled pipe. The pipe is almost touching the wood fascia. I have the one inch clearance from the roof sheathing but I dontThink I have one inch from the fascia. I'm also concerned about drafting properly.
    Jim
    David Banks Guest
    NFPA 54 12.7.2. Gas Vent Terminations.
    A.........
    B Gas vents that are over 12 inches in size or are located less than 8 ft. from a vertical wall or similar obstruction shall terminate not less than 2 ft. above the highest point where they pass through the roof and not less than 2 ft. above any portion of a building within 10 ft horizontally.
    Baton Rouge, La.
    Thanks david,
    This site Rocks when I need it.
    Quote Originally Posted by James Bohac View Post
    Jim
    Single Walled pipe clearance is 6 inches. B vent is 1 inch clearance from combustibles.
    Quote Originally Posted by David Banks View Post
    A.........
    Also IRC. 2003 M1804.2.6
    David Banks Guest
    Jim
    That single wall should not be going through the attic. Needs to be type B or L.
    Baton Rouge, La.
    My bad, That is a type B flue, however it is less than 12 inches in diameter. Does the same clearance from horizontal objects apply?
    Jim
    Jim
    Yes..