    so so, California
    Default 14s and 12s connected together in a box
    Question... looking for a NEC code that basically says two different size conducts cannot be spliced in a J box. The contractor ran 12s from the panel and in the box connected the lights and other receptacles (in the same room) to 14's. I guess he was either trying to save money or pre ran the interior wiring?
    Oct 2014
    Default Re: 14s and 12s connected together in a box
    Sorry, Marc, but the only applicable rule for a general-purpose branch circuit concerns the OC device rating. Practically, it is easy to envision someone down the road saying, "My my, your 15 amp breaker's been tripping, yet it feeds a 12AWG cable; I'll just swap it out for a 20." But that's just a reason for a cautionary note. As a contractor, i remember running 10AWG ACHH home runs to reduce voltage drop in a residence, and splicing to 12AWG ACHH in each room.
    so so, California
    Wow, great answer. I had no idea.
    But aren't the 14s overfused with a 20a disconnect?
    Thank you very much sir.
    Marc, my answer is similar, but different, than David's answer.
    The part that is similar is that the maximum OCPD is required as specified by the code for each size conductor.
    The part that is different is:
    - Splicing #14s to a #12 is not allowed if the OCPD is rated for the #12 conductors.
    Here is something to consider: how long is the circuit run (out and back)? The electrical contractor may have upsized the home runs for voltage drop considerations, in which case the OCPD 'might' be 15 amps for #12, but that creates the issue David raised about putting in a 20 amp breaker later.
    As David pointed out to an answer to a previous question of yours, the code is applicable to the installation at the time of installation, not at some future time.
    I had a few contractors (while I was working for them to inspect their homes to make sure their homes were done properly, i.e., the homes were not starter homes, the homes were $5mil to $30mil, thus trying to meet "minimum code" was not their objective), and as such, the contractor had his electrical contractor run #12 for most 15 amp circuits (except for short runs). The electrician never tried to go from the #12 home run to switches and receptacles using #14. The main thing the electrical contractor did not like was that #12 could not be backstabbed into the devices, all device connections were under the screw terminals.
    I explained the advantages of remote panels located in a central location to shorten the lengths of the circuit runs, thereby avoiding voltage drop issues when using #14 for 15 amp circuits, which they started doing. The contractors then installed the main panels in the garage (the service equipment panels were located outside) near where the heavy loads typically would be, i.e., laundry and kitchen; the remote panels would be upstairs and over by the master suites (one master suite was 3,500 sf in itself and had three bathrooms in it ... when you gotta go, you gotta go - per the owner).
    This is my third time typing this as the board returned errors, losing everything, so I will make it shorter this attempt.
    I had similar done, and suggest the contractor install a gutter/junction box next to the panel. The #10s were run into the gutter, spliced to short lengths #12s, with the #12s then run into the panel and to the OCPDs. Open the panel and 'every thing looks like it should'.
    Open the gutter and there was a note explaining what was done and why so no one messed with the #10s.
