Thread: Flex appliance connector?
-
09-24-2016, 02:53 PM #1
Flex appliance connector?
Would you categorize this as an FAC? If so, I thought the rules said you cannot run the FAC into any appliance "cabinet", which it does here.
Do you see any other issues with this?
Similar Threads:
-
09-24-2016, 09:26 PM #2
Re: Flex appliance connector?
Can't do it.
G2422.1.2.3 (411.1.3.3) Prohibited locations
and penetrations. Connectors
shall not be concealed within, or
extended through, walls, floors, partitions, ceilings or
appliance housings
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-25-2016, 06:57 AM #3
Re: Flex appliance connector?
It's wrong and I see it often..
-
09-25-2016, 08:03 AM #4
Re: Flex appliance connector?
Thank you. Does anyone know the logic of why? It helps me to understand better. Is it concerns about damage where the flex enters perhaps from vibration etc.?
-
09-25-2016, 02:11 PM #5
Re: Flex appliance connector?
Dave,
Yes. Furnaces, in particular, will vibrate during blower operation. This could result in the thin metal connector being abraded/cut through where it is fed through the furnace cabinet.
I believe there is an allowance for flexible connectors through fireplaces though. I seem to recall a grommet needs to be there to provide protection. I cannot specifically recall the code section. Probably near 2422.1.2.3
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-29-2016, 01:55 PM #6
-
10-01-2016, 10:59 AM #7
Re: Flex appliance connector?
411.1.3.3 and IRC G 2422.1.2.3
Exception # 4 allows the listed appliance connector to enter the appliance to connect to the gas valve when protected by rubber grommet, plastic sleeve etc. to protect it from vibration from the motor.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
10-02-2016, 03:17 PM #8
Re: Flex appliance connector?
The flex connector is used on Lennox Pulse furnaces because of the vibration, hard piping to a Pulse is not allowed. There are to be vibration eliminators in the gas line the supply and return duct, and the intake and exhaust have mufflers to control the noise. The flex connector is allowed around here by local jurisdiction because the door comes off easy and there is a rubber grommet used. This is not an issue around here and the connection will not come loose, a gas dryer vibrates more than a furnace and a flex is used there all the time.
Dan Hagman ACI