Results 1 to 7 of 7
Thread: Twilight Zone
-
05-17-2007, 10:50 AM #1
Twilight Zone
I had the broker run this one for me. Good name Huh?
Similar Threads:
-
05-17-2007, 11:40 AM #2
Re: Twilight Zone
Nice name. Romex wire to garbage disposal should be secured and in conduit (FMC) for protection against physical damage.
-
05-17-2007, 04:27 PM #3
Re: Twilight Zone
Ahh, Mr. Banks.... always the inspector! Good call ! Great name, you're right.
-
05-17-2007, 05:17 PM #4
Re: Twilight Zone
NM conductor (Romex) is non-code complying as an appliance connector.
I too like the name on that GD and think it would be excellent tool for disposing of really obnoxious agents?
Jerry McCarthy
Building Code/ Construction Consultant
-
05-18-2007, 07:57 AM #5
Re: Twilight Zone
What Jerry said. Putting Romex® in flexible conduit protects it from "physical damage" but not from motion/vibration. Code-required flexible cord has stranded conductors - that will not break after being bent back and forth multiple times.
- BOB
-
05-18-2007, 06:33 PM #6
Re: Twilight Zone
-
05-18-2007, 07:22 PM #7
Re: Twilight Zone
I was agreeing with Jerry that Romex® is not approved. I did not mean to imply that Jerry said the rest of what I wrote.
The code does not explicitly require flexible cord. I should have said that the code effectively prohibits using NM cable by 314.15 (A) To Follow Surface. NM cable in flexible conduit would seem to be prohibited by 314.15 (B) Protection From Physical Damage. (Where only non-flexible conduit is allowed for protecting NM from physical damage.)
Flexible cord (with a plug connection) is allowed (but not required) by 422.16 (B) (1) Electrically Operated Kitchen Waste Disposers.
I should not have said "code-required". Flexible conduit with individual conductors can be used. The overwhelming majority of code-compliant installations I have seen use flexible cord and plug.
- BOB