Results 1 to 20 of 20
12-19-2008, 11:09 AM #1
Double pole 220 volt breaker used for 110 circuit
Can a 20 amp double pole breaker that is designed for a 220 volt circuit be used for a single 110 volt circuit? Like the one in the photo.
12-19-2008, 11:18 AM #2
Re: Double pole 220 volt breaker used for 110 circuit
Yes, but ...
What's with all those disconnected wires hanging around there? That is truly unsafe.
12-19-2008, 09:24 PM #3
why not look at a the listing
12-20-2008, 08:30 PM #4
Yeah, what's with the two loose conductors? Also the top breaker has a broken throw and looks to be double tapped on the top side. Hard to tell from the photo.
12-21-2008, 11:35 AM #5
Barry, your double tap is a shadow.
12-21-2008, 02:42 PM #6
Will it work...yes recommended no.
but ....
Open splices and damaged breaker above.
Have electrician further review and improve.
Michael Almeida
Home Inspection in Southern Bergen, Hudson & Essex County by Pillar To Post
12-22-2008, 06:59 AM #7
Yes, The circuit will function; however it is a definate sign of non-professional work, the 2-pole breaker is not being used for its intended design and should be recommended to be replaced with a single pole. The two disconnected circuits are a different matter.
12-22-2008, 07:08 AM #8
no brainer put cover on box inform client to have qualifed electrician inspect box has a lot of problems as for 220 being used for 110 no
12-22-2008, 07:19 AM #9
12-28-2008, 10:21 AM #10
So now we have a yes and a no for the question.
12-28-2008, 10:27 AM #11
12-28-2008, 07:02 PM #12
12-28-2008, 07:07 PM #13
12-28-2008, 07:13 PM #14
Maybe that is what he was talking about, but I read that as "as for 220 being used for 110 no", i.e., you do not use 220 volts for 110 volt circuits, but now I see he was saying it meaning "as for 220 volt breakers beings used for 1 - 110 volt circuit, no", which, of course, is incorrect as each side of the breaker only has 120 volts, so using only one side for 1 - 120 volt circuit is not a problem.
Guess I need to improve my reading-between-the-lines comprehension skills.
12-29-2008, 08:11 AM #15
C'mon Jerr I don't even think you needed to read between the lines to figure that one!
12-29-2008, 03:14 PM #16
Brian,
I tend to think in complete sentences, I also tend to write in complete sentences, so when I read something like:
*I* *HAVE TO MAKE IT INTO* complete sentences to understand what has been written. Sometimes I win on understanding them, sometimes I lose on understanding them. I lost this time.
01-01-2009, 02:09 PM #17
interesting salvage;There has to be better ways to save money and respect.
Does not the 220 breaker have one switch , that is internally
disconnecting both wires? and if so , as used as two 110 circuits , if one of the 110
lines was over loaded , would not both wires be disconnected?
01-01-2009, 03:13 PM #18
No, two internal switches, both operated by the same handle and internal trip mechanism, but two separate switching devices.
Yes, that would be the intent when using a double pole internal trip (or external trip) on a multiwire circuit: it shuts off the power to both 120 volt legs.that is internally disconnecting both wires? and if so , as used as two 110 circuits , if one of the 110 lines was over loaded , would not both wires be disconnected?
01-05-2009, 10:32 AM #19
Check the UL listing book for that particular circuit breaker, and if UL has approved that particular 2-pole breaker, for use as single pole, then its use is "approved". if not, then it is "not approved".
Jim Hays
01-14-2009, 10:18 AM #20
Few days ago at a inspection the DIY installed a 20 amp double pole breaker to supply the basement receptacles they finished. Somewhere along the line they must of split it for two circuits and tied the grounds and neutrals together.
I wonder if they where related to the other post that was asking questions on how to wire his basement............