Results 1 to 3 of 3

Thread: AFCI Exception

  1. #1
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default AFCI Exception

    I inspected a home that had new service equipment.

    I noticed that there were no AFCI breakers in the panel. I questioned this and the electrician told me that an amendment was made to the electrical code that states - AFCI breakers are not required for a service upgrade??

    Can anyone confirm and provide the language for this exception?
    Thanx

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: AFCI Exception

    There is no exception because there is no requirement.

    Replacing the service has nothing to do with the circuits needing AFCI protection.

    *Installing new circuits* would be different, were any "new" circuits installed? If so, *those* new circuits would require AFCI protection.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: AFCI Exception

    There does appear to be a violation of the requirement for the cables to be secured within 12" of the panel.