    I saw this connection between 2 water heaters and was wondering what it is and what it does. Anyone know? I think its called a water circiulation pump as that was written on the wall next to it.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Water Circulation Pump

    How were the top pipes connected?

    This is a diagram of a hot water circulation system.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Brian Kelly's Avatar
    Brian Kelly Guest

    Default Re: Water Circulation Pump

    Quote Originally Posted by Stephen G Sheldon View Post
    I saw this connection between 2 water heaters and was wondering what it is and what it does. Anyone know? I think its called a water circiulation pump as that was written on the wall next to it.

    It circulates water


  4. #4
    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest

    Default Re: Water Circulation Pump

    I'm not sure how the top pipes were connected. What is the purpose of this? Why do you not see it more often?


  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Water Circulation Pump

    Instant hot water, no waiting for water to come from the storage tanks. It keeps water circulating in the system so when you turn on the tap you wait seconds rather than minutes for hot water to arrive.
    You don't see more of them because they cost money to install and operate! Pretty much standard in upper end houses. Almost all multifamily with central plants have a form of this system. Can you imagine having to be the first one to turn on the hot water if the plant was 300-400 feet away and the pipe was large enough to serve 5-10 units? You could wait all day, but keep water circulating and you get hot water when you want it.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Water Circulation Pump

    Quote Originally Posted by Stephen G Sheldon View Post
    What is the purpose of this? Why do you not see it more often?
    Quote Originally Posted by Jim Luttrall View Post
    Instant hot water, no waiting for water to come from the storage tanks. It keeps water circulating in the system so when you turn on the tap you wait seconds rather than minutes for hot water to arrive.
    Jim is correct.

    You don't see more of them because they cost money to install and operate!
    You don't? You should. I am surprised as, while it does cost more to install and cost a little (not much) to operate, the water savings in gallons of wasted water used not only offsets that cost but, in the areas with droughts, is wasting A LOT of precious water, leaving the running the water just to get hot water.

    Forget about those 1.6 gpf double-flusher and think of all the water wasted down the drain just waiting for hot water to arrive.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest

    Default Re: Water Circulation Pump

    I appreciate your explanation. Thanks.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Water Circulation Pump

    Also note that some of those circulation pumps, not sure about that particular one, MUST have the shaft for the pump motor oriented horizontally.

    Looks like this one: http://www.taco-hvac.com/uploads/Fil...ry/102-135.pdf

    Under Installation (bold underlining is mine): "2. Mounting position – Circulator must be mounted with the motor in a horizontal position. It may be mounted vertically with the motor up, provided that the system cold fill pressure is at least 20 psi (138 kPa)."

    Last edited by Jerry Peck; 05-09-2009 at 07:20 AM.
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9

    Default Re: Water Circulation Pump

    You should also make sure the pump is meant for potable water & not a recirculating pump meant for hydronic systems, the pumps used on the hydronic systems look the same & are cheaper, but they do not have the stainless steel recirculating blades & will leave a rusty residue in the water.

    Clarksville Home Inspection
    JW Goad
    TN License #307 | KY License #2402

  10. #10
    Rob Turner's Avatar
    Rob Turner Guest

    Default Re: Water Circulation Pump

    It helps keep well to do people from having to wait for their hot water. The extra costs come in on water heater fuel consumption. Because of the circulation of hot water through the pipes, heat is lost. Gas water heater burners come on alot more often. The result is an increased fuel bill.


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Water Circulation Pump

    Quote Originally Posted by Rob Turner View Post
    It helps keep well to do people from having to wait for their hot water. The extra costs come in on water heater fuel consumption. Because of the circulation of hot water through the pipes, heat is lost. Gas water heater burners come on alot more often. The result is an increased fuel bill.

    With the hot water pipes being insulated as required, there is not that great of a waste of energy, but, yes, it does cost more, however, I keep going back to ... it sure beats wasting all that water ... which is in short supply in many areas all over the country.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Water Circulation Pump

    Does anyone have a good way to test if the pump is working? Many times I find the pump after I have tested all of the fixtures in the house and I have no idea when the hot water was used last.


  13. #13
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: Water Circulation Pump

    Come back the next day, or change your routine so you inspect the water heater earlier during the inspection. I don't know if there is an easy way once you've been in the bathrooms already.

    Jim Robinson
    New Mexico, USA

  14. #14
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Water Circulation Pump

    Quote Originally Posted by Jim Robinson View Post
    Come back the next day, or change your routine so you inspect the water heater earlier during the inspection. I don't know if there is an easy way once you've been in the bathrooms already.
    Maybe I need to add " Seller and sellers family MUST NOT BATHE OR USE HOT WATER PRIOR TO INSPECTION!"?


  15. #15
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Water Circulation Pump

    Quote Originally Posted by Vern Heiler View Post
    Does anyone have a good way to test if the pump is working?

    You mean if it runs, or if it actually does what it is intended to do?

    To see if it runs:
    - First make sure it is plugged in ( I know, but you have no idea how many I have found NOT plugged in and the seller did not know it).
    - Then unplug it and test the receptacle to make sure there is power, plugging it back in afterward.
    - Then, if there is no timer on it (some have built-in timers on them and others do not) if it is plugged in it should be running. You will feel the slight vibration from the motor running as different than when it was unplugged and not running.
    - If there is a timer, you will need to deal with the timer, or just report as being their, with a timer, not checked for operation.
    - Sometimes there will be service valves which allow the pump to be taken out of service and replaced without shutting the water to the water heater off - make sure they are open (like the un-plugged ones, I have found some left with the valves closed and the seller did not know it).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  16. #16
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Water Circulation Pump

    Quote Originally Posted by Jerry Peck View Post
    You mean if it runs, or if it actually does what it is intended to do?

    To see if it runs:
    - First make sure it is plugged in ( I know, but you have no idea how many I have found NOT plugged in and the seller did not know it).
    - Then unplug it and test the receptacle to make sure there is power, plugging it back in afterward.
    - Then, if there is no timer on it (some have built-in timers on them and others do not) if it is plugged in it should be running. You will feel the slight vibration from the motor running as different than when it was unplugged and not running.
    - If there is a timer, you will need to deal with the timer, or just report as being their, with a timer, not checked for operation.
    - Sometimes there will be service valves which allow the pump to be taken out of service and replaced without shutting the water to the water heater off - make sure they are open (like the un-plugged ones, I have found some left with the valves closed and the seller did not know it).
    Thanks Jerry. I too have found them unplugged, and was pretty confident it was not working. You must have the touch of a safe cracker to feel that little motor inside that large casting. I have never felt a thing! Maybe they were all dead?


  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Water Circulation Pump

    Quote Originally Posted by Vern Heiler View Post
    You must have the touch of a safe cracker to feel that little motor inside that large casting. I have never felt a thing! Maybe they were all dead?
    Shoot, most of them I could even hear running.

    If you cannot feel it, set a cup of water on it, the vibration will show in the surface of the water in the cup. If the surface is still, it is most likely not running. Note that I have never tried this test for those pumps, but it works for everything else, so it should work for them too. Does not take much vibration at all to resonate in the water and show in the surface of the water. I'd try a Styrofoam cup first as the vibration against the bottom should make the bottom act like a drum beating back and forth and really get the water moving, however, if it has the opposite effect and dampens the vibration in the foam sides, then try a rigid plastic or metal cup.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Water Circulation Pump

    I'll try that and let you know.


  19. #19
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: Water Circulation Pump

    Quote Originally Posted by Stephen G Sheldon View Post
    I saw this connection between 2 water heaters and was wondering what it is and what it does. Anyone know? I think its called a water circiulation pump as that was written on the wall next to it.
    There is one problem with the installation of that recirculation system. It is returning the water to both tanks in a parallel connection. The problem is the piping after the tee, it should be an equal distance with equal fittings between each water heater. The corrugated copper quick connect line adds lots of flow resistance which also contributes to the system to be out of balance. They way its plumbed in now the one water heater is doing all the work which will shorten that tanks life.

    My preferred way of installing two heaters in parallel is the first in last out method. Here is a PDF of what it would look like. http://www.bradfordwhite.com/images/...ng/2H_TCRC.pdf Nice thing about this set up is you can isolate and shut down a heater if one does start to leak. The recirculation line returns back to the cold of both heaters with out modifying the drain valves


  20. #20
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: Water Circulation Pump

    One more note. check with the local codes on the gas piping. In Illinois the gas piping must be hard piped to the heater. Also I noticed the heater on the right is newer. I would really like to see a picture of how it is plumbed in on the top. If they attempted to plumb it in parallel, the home owner will have one of the two heaters fail prematurely.