    Ok this is from Heny the 5th's castle. 800 amp service, with 10 panels. All but two were in great condition. Several wires in the panel are capped, although they appeared to be live. Futhermore, does the penetraion in pic 1 require a clamp? Missing bushings and multiple cables through penetration noted.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Distribution panels

    That is a conduit fitting in pic #1, not a cable. No clamps required on the conductors.

    Those are not missing bushing. Bushing protect the conductors. Those would be missing clamps. Clamps would properly secure the cables to the enclosure. Most clamps for the 12-x and 14-x cable sizes are rated for use with 2 or less cables, but the package would need to be checked to confirm.

    The grounding wires into the lug is also incorrect. Lugs like that are for 1 conductor.


  3. #3
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Distribution panels

    That conduit in picture 1 - If those conductors are larger then # 4 awg then a bushing is required, if smaller then # 4 no bushing required


  4. #4
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Distribution panels

    In pic 5 I could not figure out why the capped wires were live. Any thoughts.


  5. #5
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Distribution panels

    I assume you traced each of the conductors out, are you sure one of them is not terminated on a breaker?
    If not it would seem that someone is using the panel as a raceway?


  6. #6
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Distribution panels

    Ken,
    I did trace each wire and the race way is the only explanation I can come up with because the wires were def. live.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Distribution panels

    Quote Originally Posted by mathew stouffer View Post
    In pic 5 I could not figure out why the capped wires were live. Any thoughts.
    Possibly to a pool light switch in the house, and back to the panel, then out to the pool light transformer, or something similar.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Distribution panels

    ah yes that makes sense. There was pool lighting all over the place.


  9. #9
    Join Date
    Apr 2009
    Location
    Manchester, Vermont
    Posts
    298

    Default Re: Distribution panels

    Mathew Stoffer did you get all the answer you where looking for?

    What I notice in picture five, was two splices.

    I believe if you trace the two black wires back, you find then connected to a double pole circuit breaker? Well that just a guess on my part.