Results 1 to 22 of 22
Thread: Flex connector below cabinet?
-
08-30-2009, 09:27 AM #1
Flex connector below cabinet?
Are flexible connectors allowed to routed below kitchen cabinets? This connector is for a gas cooktop. Obvious concerns are physical damage from items being stored below.
Similar Threads:
-
08-30-2009, 04:49 PM #2
Re: Flex connector below cabinet?
Trent,
Flex connectors can not be routed through anything, cabinets, walls or partitions. They can go from a shut off to the appliance.
NFPA 54 9.9.1.8 2006 edition
Jack
-
08-30-2009, 05:07 PM #3
Re: Flex connector below cabinet?
They do need to be attached to the back wall. Supports/protect.
Not a very neet Install job.
Best
Ron
-
08-31-2009, 04:16 AM #4
Re: Flex connector below cabinet?
TT: Photo #2 shows a disallowed installation.
G2422.1.2.3(411.1.3.3) Prohibited locations and penetrations.
Connectors shall not be concealed within, or extended
through, walls, floors, partitions, ceilings or appliance housings.
As to the physical damage concerns, it is a judgement call:
G2422.1.1 (411.1.2) Protection from damage.Connectors
and tubing shall be installed so as to be protected against physical
damage.
-
08-31-2009, 09:13 AM #5
Re: Flex connector below cabinet?
That would have been a simple install with black pipe. A tee, nipple, cap, an two lengths and you're done.
Looks a bit amateur if you ask me - I wonder if it was installed by the appliance vendor.
-
08-31-2009, 10:13 AM #6
Re: Flex connector below cabinet?
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
08-31-2009, 10:30 AM #7
-
08-31-2009, 05:03 PM #8
Re: Flex connector below cabinet?
OK I am easily confused so please explain. It is hard piped into the cabinet. Flex csst pipe is then run up through the shelf to the stove top.
Damage to the flex could possibly occur from placing items in the cabinet. I don't like the idea of the flex running through the shelf but I see nothing that says you can't. 1/2" clearance around the diameter of the tube is required. Floppy steel conduit could protect it. CSST approves running through cabinets, walls, floors, etc.
Is the code talking about "appliance connector" not running through partitions, etc. ?
I see flex in cook top cabinets all the time in all new construction, should this be called out.
I see this run through the floor into fireplace compartments?
I see it run through walls, joist, etc.?
Last edited by Mike Schulz; 08-31-2009 at 05:15 PM.
-
08-31-2009, 06:43 PM #9
Re: Flex connector below cabinet?
Mike,
Let me tell you all of the ways I am confused... Never mind, I won't.
The flex in the pic is not CSST, it is a flexible appliance connector. CSST is approved to run through walls, flexible connectors are not.
Yes, the connector could be damaged by pots & pans. As AD said, it really isn't addressed in the code. As for through the shelf, I think it is a matter of interpretation. "Partition" might cover shelves.
I believe it should be reported, if the flex is run through the cabinet. I have only seen the flex connected to a pipe fitting under the cook top, which is fine.
I believe that should be reported.
Once again, I believe it should be reported.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
08-31-2009, 07:03 PM #10
Re: Flex connector below cabinet?
That piece running into the wall is a connector. Black pipe should have extended into the cabinet to allow access for repair. The rest is OK but csst needs protection. AND I always recommend installation of EFV(excess flow valves) as well as bonding. Was it bonded?
Also, that cssst hanging against an outlet is also a BAAAAAAAAAAAD idea.
-
08-31-2009, 07:48 PM #11
Re: Flex connector below cabinet?
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
08-31-2009, 10:42 PM #12
Re: Flex connector below cabinet?
Flexible appliance connector listed to ANSI Z21.24. This is NOT CSST. Gunnar, Aaron, et al get a gold star.
Bob
Keep the fire in the fireplace.
-
09-01-2009, 08:24 AM #13
Re: Flex connector below cabinet?
Thanks Gunnar, the confusion came in because It looks like CSST, it all makes sense now. How can you see from those pictures that its not csst?
-
09-01-2009, 08:44 AM #14
Re: Flex connector below cabinet?
Mike,
The yellow sheath on CSST is, umm, a sleeve that can be cut/removed. Actually, it must be cut back to allow the brass fitting to be attached. The yellow coating on the appliance connector is adhered, like it is factory sprayed or dipped. The flexible appliance connectors have the brass fittings attached. Primarily, I have never seen CSST used between the gas shutoff valve and an appliance. It is used as a piping material instead of black iron.
If you go to the gastite website, you should be able to see the difference.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-01-2009, 10:16 AM #15
Re: Flex connector below cabinet?
Now that you pointed that out it comes to light for me. here is what I am use to seeing in new construction and the appliance connector is quite distinguishably different.
-
09-01-2009, 10:17 AM #16
Re: Flex connector below cabinet?
dang it, I keep forgetting to add the picture......argggg
-
09-01-2009, 10:21 AM #17
Re: Flex connector below cabinet?
I was off only 2 KB and it would not upload. I think more people would post if they did not have to spend so much time resizing pictures. I know it holds me back from contributing.
-
09-01-2009, 10:32 AM #18
Re: Flex connector below cabinet?
Mike,
Yes. I forgot to mention that some are uncoated (like the one in your pic), some are yellow coated and I have also seen black coated. Not sure, but I assume different manufacturers use different colors.
Someone posted a link to an online utility that will resize pictures. I cannot recall the name of the site. I tend to take small pics because they are only 3" in my reports, so a large pic is pointless.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
09-01-2009, 01:03 PM #19
Re: Flex connector below cabinet?
Bob,
Is that an acceptable location for that regulator?
Trent,
That cord and plug set should not go through the cabinet either.
-
09-01-2009, 01:12 PM #20
-
09-01-2009, 02:07 PM #21
Re: Flex connector below cabinet?
-
09-01-2009, 02:35 PM #22
Re: Flex connector below cabinet?
JP: And, that's just almost where I want to be . . .You are "almost right" ...




Reply With Quote


Bookmarks