Results 1 to 6 of 6
Thread: Help
-
11-10-2009, 10:36 PM #1
-
11-10-2009, 10:39 PM #2
Re: Help
what is green and is found in a panel?

-
11-10-2009, 11:51 PM #3
Re: Help
What Wayne said. It does look like you're missing a wire clamp though.
-
11-11-2009, 05:30 AM #4
Re: Help
Your bond is right in front of you - the grounding conductors .
You are missing the proper Cable connector and the reidentifying of the white conductor to indicate it is a phase conductor as oppossed to a neutral conductor.
I am basing this on your saying it's an AC subpanel, which I assume you are talking about a 240 volt disconnect for an Air Conditioning unit
-
11-11-2009, 05:16 PM #5
Re: Help
Scott,
First things first ...
That is on a house and not a submarine, therefore it is not a subpanel but simply a panel.
Secondly, that is a 240 volt circuit which does not need a neutral, however, the white conductor is not permanently re-identified as is required when white conductors are used as hot conductors.
The enclosure is grounded by the attachment of the ground.
The NM cable is required to be in a clamp.
-
11-11-2009, 06:17 PM #6



Reply With Quote

Bookmarks