Furnace / Boiler Shutoff Location
What is the standard for the location of of the service power switch on a boiler and furnace?
I am seeing them at doorways to the basement and more often, on the unit themselves.
What should be called out?
Similar Threads:
-
03-10-2010, 08:06 PM #2
Re: Furnace / Boiler Shutoff Location
both are needed. At the top of the stairs for an emergency shutdown and by the unit for the tech
-
03-11-2010, 06:30 AM #3
Re: Furnace / Boiler Shutoff Location
I see, Is there a date that this rule came into play?
Does anyone have documentation on this?
I always like to be able to back up my findings.
Thank you for the info.
-
03-11-2010, 08:25 AM #4
Re: Furnace / Boiler Shutoff Location
I'm not aware of a disconnect required at the top of the stairs but one is required at the unit itself or within site.
TABLE E4001.5
DISCONNECTING MEANSAir-conditioning condensing units and heat pump units.A readily accessible disconnect within sight from unit as the only allowable
means. *a
a. The disconnecting means shall be permitted to be installed on or within the unit. It shall not be located on panels designed to allow access to the unit.
-
03-11-2010, 09:39 AM #5
Re: Furnace / Boiler Shutoff Location
What is this 'basement' that you guys are speaking of. Just at the unit itself around here, unless you count the breaker panel as a shut off. Generally just a plug that can be removed from the receptacle outlet.
Jim Robinson
New Mexico, USA
-
03-11-2010, 10:39 AM #6
Re: Furnace / Boiler Shutoff Location
Thank you Wayne, what is that from? NRC?
Jim, A basement is one or more floors of a building that are either completely or partially below the ground floor.
-
03-11-2010, 10:41 AM #7
Re: Furnace / Boiler Shutoff Location
You're welcome!
It's actually from the 2006 IRC but the NEC has the same wording or real close to it!