Results 1 to 7 of 7

Thread: Detached garage

  1. #1
    Join Date
    Mar 2007
    Location
    Daniel Island, SC.
    Posts
    240

    Default Detached garage

    Hello,

    What is the distance that a detached garage has to be from the main house to not have sheetrock or a fire barrier in the garage? Inspected a detached garage today that had a plywood ceiling and pegboard walls over studs.

    Thanks,

    Jim

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Detached garage

    (bold and underlining are mine)
    - R309.2 Separation required. The garage shall be separated from the residence and its attic area by not less than 1/2-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Type X gypsum board or equivalent. Where the separation is a floor-ceiling assembly, the structure supporting the separation shall also be protected by not less than 1/2-inch (12.7 mm) gypsum board or equivalent. Garages located less than 3 feet (914 mm) from a dwelling unit on the same lot shall be protected with not less than 1/2-inch (12.7 mm) gypsum board applied to the interior side of exterior walls that are within this area. Openings in these walls shall be regulated by Section R309.1. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Detached garage

    Points to ponder.

    The part Jerry Peck quoted is often ammended when the IRC is adopted by certain jurisdictions, and also often more locally ammended with more strict provisions regarding proximity to residence or other strutcures on the same lot. It is common to see local ammendments to for example 5/8" gyp minimum rather than 1/2", and other ammendments/enhancements to the unammended IRC.

    Furthermore, local ammendments, and/or zoning codes, set back provisions, etc. may further require when that detached garage is closer to a lot line, or a neighboring lot's structure is encoraching on a set-back or set-off from a lot line.

    Overhangs and projections count when measuring those distances between structures and/or lot lines or set-back lines.


  4. #4
    mike huntzinger's Avatar
    mike huntzinger Guest

    Default Re: Detached garage

    does this count as a detached garage

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  5. #5
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Detached garage

    Quote Originally Posted by mike huntzinger View Post
    does this count as a detached garage
    Is that a movie set?

    The beatings will continue until morale has improved. mgt.

  6. #6
    mike huntzinger's Avatar
    mike huntzinger Guest

    Default Re: Detached garage door

    found this over the fence at an inspection, no walls no roof


  7. #7
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Detached garage

    Quote Originally Posted by mike huntzinger View Post
    does this count as a detached garage
    It's an attached garage wannabe.

    Probably to prevent neighbor complaints, bylaw violation, because of a project car or something similar. In my area, it would be a blue tarp.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •