Results 1 to 4 of 4
  1. #1
    dan orourke's Avatar
    dan orourke Guest

    Default Disconnect switch - hot tub

    Last edited by dan orourke; 01-01-2008 at 03:53 PM.
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Disconnect switch - hot tub

    Quote Originally Posted by dan orourke View Post
    A disconnect switch is suppose within sight of the hot tub (not within 5 feet) correct?
    Correct.

    From the NEC. (underlining is mine)
    - 680.41 Emergency Switch for Spas and Hot Tubs.
    - - A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings.

    There was a metal electrical junction box within 5 feet of the hot tub with a metal cover plate. I think this was suppose to be the disconnect switch, but they never got around it.....
    Or someone told them it could not be within 5 feet of the spa, so they removed it and just did not bother installing another one in the proper location.

    Now, the metal window frames and that metal electrical junction box within 5 feet of the hot tub should be bonded with the hot tub bonding system, correct?
    Correct.

    Basically all permanently installed metallic items larger than 4" in the smallest dimension located within 5 feet of the spa and located less than 12 feet above the spa out to the 5 foot perimeter around the spa (like a big box placed over the spa). This includes metal window frames, gutters, drip edge, metal doors (not sliding glass doors themselves, but their tracks), hose bibbs, etc.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Disconnect switch - hot tub

    I was wondering how I missed this all these years, then I saw the last part of Jerry's post.

    From the NEC. (underlining is mine)
    - 680.41 Emergency Switch for Spas and Hot Tubs.
    - - A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings
    No switch required, right?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Disconnect switch - hot tub

    Jim,

    You are correct.

    The idea is that on a spa or hot tub location other than a home, it is now recommended that the spa motor not be on or circulating water for an " X "
    amount of time. I think is like every 15 or 20 minutes, the pump is supposed to shut down for a cool down period to prevent persons from sitting in the heated water for an over extended period of time.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •