Concentric vent termination
I need some input here. I see several direct vent pipe that seem too low. We do get heavy snow at time that may cover a pipe if its like this one.
I think these vents should be at least 12" above ground but can't find documentation.
Any help would be appreciated.
Similar Threads:
-
12-24-2011, 11:17 PM #2
Re: Concentric vent termination
Although many are similar, you should check the manfacturer's specs for the particur device.
http://www.rinnai.us/documentation/d...al)_3-2011.pdf
Check out page 18. Remember, all dimensions are above snow line.
-
12-25-2011, 12:18 AM #3
Re: Concentric vent termination
This forum does not really allow local PDF posting very well however here is an excerpt from one of mine.
1CT0302 / 1CT0303
CONCENTRIC VENT TERMINATION
FOR CATEGORY IV FURNACES
12" above anticipated snow level or grade.
-
12-26-2011, 05:03 PM #4
Re: Concentric vent termination
Thanks Steve and Bob. I knew there was something somewhere about 12", just couldn't find it. I will include this diagram in report. It would seem that common sense tells us to put the vent above snow line, but then it's amazing what we see sometimes.
By the way there are 2 stones lodged down in the pipe. Can't imagine how that happened.
-
12-27-2011, 06:50 AM #5
Re: Concentric vent termination
Yes, common sense tells one to put it above snow levels. Ya don't need no stinkin reference document.
-
12-27-2011, 07:25 AM #6
Re: Concentric vent termination
The reason I included the link is so you can see that there are additional clearances to consider. Check them out.