04-16-2012, 12:50 PM #1
Why the Metal Posts to support what?
Help me out here, I don't see what this is supporting and why, kitchen is above the posts and the supporting part above the post is nailed to the Engineered I-Type joists. Looks strange to me and this is new contruction that is all done. The load bearing walls are about 5' both directions. These are 2X14 I-Type Joists.
Similar Threads:Dan Hagman ACI
ProSite Home Inspections
Des Moines, Iowa
04-16-2012, 01:03 PM #2
04-16-2012, 04:21 PM #3
Re: Why the Metal Posts to support what?
Dan,
I agree with John, appears to be for one super heavy load just above the post.
If its a new house have the builder explain why it there if you can't.
04-16-2012, 04:24 PM #4
Dan Hagman ACI
Des Moines, Iowa
04-17-2012, 07:28 AM #5
Just an observation, If the I-Joist cannot support the load of the Island above, contractor probably should have done a drop beam under the joists (for the length of the island) and installed squash blocks above as per I-joist manufactures instructions. Just my opinion.
04-17-2012, 03:10 PM #6
Dan Hagman ACI
Des Moines, Iowa
04-19-2012, 09:10 AM #7
The I-joists might be strong enough to support the granite. The builder may have just wanted a "belt and suspenders" approach.
04-20-2012, 04:59 AM #8
post needs to be secured properly if it is used!
http://www.jjeffzehnder.com/
04-20-2012, 05:35 AM #9
Being new construction, this mod likely was engineer designed or approved. No need to second-guess the engineer. The CI would have approved based on the engineer letter.
04-20-2012, 05:48 AM #10