Re: Simson HUCQ
Hello Doug,
Although not specifically made for that purpose we do see it used here as well. The AHJ has not disapproved its use. Simpson does manufacture the LSC for stringer attachment but it is not often seen. The HUCQ is a very heavy duty hangar suited for the potential loads a stair could incur.
Obviously it will be the AHJ call but part would most likely be using the notching limitations of IRC R502.8 and/or any specific CA requirements. You might also ask to see, or advise the client to check, any engineered plans for the home. It is possible the Engineer specified its use in that manner.
It is worth giving Simpson Strong-Tie a call as they are very helpful with answering any technical questions in regards to their products.
-
09-30-2011, 08:28 AM #4
Re: Simson HUCQ
You need to calculate the load on that stringer and then check the Simpson catalog table to see if it can carry the calculated load.