Ran into a multi-wire branch circuit on same leg in the panel. Since this is on one leg you have a cumulative effect on the neutral.
I was not able to find anything in the NEC that says this is not allowed other than common sense say bad idea and that you want to size the neutral in accordance of the load.
Anyone have in more info to share on this?
Similar Threads:Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
 - 
	04-26-2012, 08:12 AM #2
 Re: Multi-Wire Branch circuit on same leg
		You are correct that this will create an additive current on the neutral and could potentially overload it. Worst case it could be carrying 2x the rated current of the circuit.
The current NEC requires the conductors of a MWBC to be grouped on a 2 pole breaker.
All answers based on unamended National Electrical codes.
 - 
	04-26-2012, 08:57 AM #3
 Re: Multi-Wire Branch circuit on same leg
		There are two code violations. The neutral would be undersized, and the ungrounded conductors would be considered paralleled.
Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
 - 
	04-26-2012, 09:00 AM #4
 Re: Multi-Wire Branch circuit on same leg
		I thought I saw this not too long ago, because the breakers were not adjacent to each other. But looking at the panel diagram, it turned out to be OK. The tandem breakers can fool you.
The problem with my setup was no tie-bar and no way to install a factory tiebar.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
 - 
	04-26-2012, 10:08 AM #5
 Re: Multi-Wire Branch circuit on same leg
		I should of mentioned this was on a tandem breaker.
Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
 - 
	04-26-2012, 10:14 AM #6
 Re: Multi-Wire Branch circuit on same leg
		Some tandems will allow the two circuits to be on opposite legs in the panel. IIRC GE is one, most of the other brands do not catch both legs.
All answers based on unamended National Electrical codes.
 - 
	04-26-2012, 10:18 AM #7
 Re: Multi-Wire Branch circuit on same leg
		Thanks Jim this was a Square D so on single leg.
Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
 - 
	04-26-2012, 11:11 AM #8
 Re: Multi-Wire Branch circuit on same leg
		
 - 
	04-26-2012, 11:17 AM #9
 - 
	04-26-2012, 11:43 AM #10
 Re: Multi-Wire Branch circuit on same leg
		This was a xxxx4040 panel so no tandem would be allowed.
I was after code info on having a MWBC on the same leg. When I read the NEC I was not clear so I threw it out to the masses to get some perspective and possible code reference that states thy must be on different legs.
Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
 - 
	04-26-2012, 12:27 PM #11
 Re: Multi-Wire Branch circuit on same leg
		Correct on the no tandem Don.
All answers based on unamended National Electrical codes.
 - 
	04-26-2012, 01:16 PM #12
 - 
	04-26-2012, 03:18 PM #13
 Re: Multi-Wire Branch circuit on same leg
		- 210.4 Multiwire Branch Circuits.
- - (A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.
- - - FPN: A 3-phase, 4-wire, wye-connected power system used to supply power to nonlinear loads may necessitate that the power system design allow for the possibility of high harmonic currents on the neutral conductor.
- - (B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
- - (C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
- - - Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
- - - Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
- - - - FPN: See 300.13(B) for continuity of grounded conductor on multiwire circuits.
- - (D) Grouping. The ungrounded and grounded conductors of each multiwire branch circuit shall be grouped by wire ties or similar means in at least one location within the panelboard or other point of origination.
- - - Exception: The requirement for grouping shall not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious.
- Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
If the multiwire branch circuit is connected to the same bus, it will not have voltage between the ungrounded conductors, and as this is a requirement by definition, the circuit would not be a multiwire branch circuit, it would be an incorrectly wired circuit.
 - 
	04-26-2012, 03:57 PM #14
 Re: Multi-Wire Branch circuit on same leg
		I saw a reply indicating they could still be on separate legs. When you see this just check w/ an elec. meter that reads the voltage. One lead on each C/B termination. If no voltage, you are right about the neutral overload potential / incorrect installation. If 240 volts, it's OK. A handle tie is not necessarily required, if two separate 120 volt circuits and installed before that requirement. Still a good idea to have and recommend the tie though.
 - 
	04-26-2012, 04:29 PM #15
 - 
	04-26-2012, 05:21 PM #16
 Re: Multi-Wire Branch circuit on same leg
		Jerry, Thank you that was what I was looking for and missed.
Thanks all for the comments.
Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
 - 
	04-26-2012, 05:23 PM #17
 Re: Multi-Wire Branch circuit on same leg
		Prior to the 2011 NEC there was nothing to prohibit an over-sized neutral being used for two circuits on the same phase. 200.4 in the 2011 has changed that. For outdoor location it's explicitly permitted by 225.7(B).
200.4 Neutral Conductors. Neutral conductors shall not
be used for more than one branch circuit, for more than one
multiwire branch circuit, or for more than one set of ungrounded
feeder conductors unless specifically permitted
elsewhere in this Code.
 - 
	04-26-2012, 07:17 PM #18
 - 
	04-26-2012, 07:43 PM #19
 Re: Multi-Wire Branch circuit on same leg
		Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
 - 
	04-27-2012, 01:44 AM #20
 - 
	04-27-2012, 08:26 AM #21
 Re: Multi-Wire Branch circuit on same leg
		Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.
 - 
	04-27-2012, 05:46 PM #22
 - 
	04-27-2012, 08:15 PM #23
 Re: Multi-Wire Branch circuit on same leg
		Both ungrounded conductors could be tied to the same breaker (if listed for 2) and that would be OK but wouldn't make any sense. I've seen a diy job with this very setup, uggg.
A fully loaded-all capacitive load on a multi wire branch circuit may require a larger neutral under certain circumstances.
I have a double tandumdum Siemens breaker in my truck that I bought decades ago thinking it might come in handy. It is setup to install 2 multi wire branch circuits.
Looks like I'm going to have it when it becomes a collectors' item
 - 
	04-28-2012, 05:50 PM #24
 Re: Multi-Wire Branch circuit on same leg
		- 240.15 Ungrounded Conductors.
- - (A) Overcurrent Device Required. A fuse or an overcurrent trip unit of a circuit breaker shall be connected in series with each ungrounded conductor. A combination of a current transformer and overcurrent relay shall be considered equivalent to an overcurrent trip unit.
- - - FPN: For motor circuits, see Parts III, IV, V, and XI of Article 430.
- - (B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit both manually and automatically unless otherwise permitted in 240.15(B)(1), (B)(2), and (B)(3).
- - - (1) Multiwire Branch Circuit. Except where limited by 210.4(B), individual single-pole circuit breakers, with or without identified handle ties, shall be permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase line-to-neutral loads.
- - - (2) Grounded Single-Phase and 3-Wire dc Circuits. In grounded systems, individual single-pole circuit breakers with identified handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.
- - - (3) 3-Phase and 2-Phase Systems. For line-to-line loads in 4-wire, 3-phase systems or 5-wire, 2-phase systems having a grounded neutral point and no conductor operating at a voltage greater than permitted in 210.6, individual single-pole circuit breakers with identified handle ties shall be permitted as the protection for each ungrounded conductor.
- - (C) Closed-Loop Power Distribution Systems. Listed devices that provide equivalent overcurrent protection in closed-loop power distribution systems shall be permitted as a substitute for fuses or circuit breakers.
 



				
				
				
					
  Reply With Quote
						
					
  I've actually heard that one before.
Bookmarks