Results 1 to 9 of 9
  1. #1
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Scorched grounding lug

    In Canada, we keep grounds and neutrals separated even in the main service panel. The grounding bus is under a cluster of wiring on the left.

    Some circuits were added, and this looked like a handy screw to mount a new lug.
    I don't know what caused this much voltage on the grounds, but I'm happy the scorch marks are there to illustrate the screw up. I had no ground on one circuit in the new suite.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  2. #2
    Garry Blankenship's Avatar
    Garry Blankenship Guest

    Default Re: Scorched grounding lug

    The reason for those burn marks can be speculated forever. I'm "guessing" that the ground bar is/was full and that little lug was created as a "sub" ground bar for a place to terminate the last few circuit ground wires. Not legal, but probably functional.


  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Scorched grounding lug

    My point is that hot spots were caused by this flaky connection. Square D provides mounting holes for these ground lugs up the sides of the panel.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Scorched grounding lug

    Looks like a good way to start a fire.

    I would wonder if this was caused by a fault condition or if an EGC is connected improperly to a downstream neutral conductor.




  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Scorched grounding lug

    Would take a lot of current on those grounds to cause that, even with the paint acting as an insulator between the incorrect terminal and washer and the enclosure - that much current on a conductor which is not intended to carry any current is a bad thing.

    That is what those look like when it takes a lightning strike - I've seen it several times after a lightning strike, even enclosure to cover through the screw and back to the enclosure through another screw.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Scorched grounding lug

    I'd really suspect someone was working on something "hot" and caused a fault. There was a tiny contact at each of the two arc marks where the contact metal got vaporized.

    I would guess none of the wires in the terminal are grounded any more with the contact points blown off and everything else painted. Prime example of why the screw is required to be in contact with the terminal and have at least two threads engaged in the metal cabinet.

    I don't know how those lugs are listed up north but here it's for one wire only.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  7. #7
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Scorched grounding lug

    I found only one ungrounded circuit but there could be a dishwasher or some other dedicated circuit there that is no longer grounded. The large solid conductor supplies a remote panel, and those circuits tested grounded, but possibly not very well. The installer may have shorted a hot to ground as a test of his handiwork, who knows?

    Bill, you are right. That is the wrong lug for that purpose, as well as being incorrectly mounted.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  8. #8
    Garry Blankenship's Avatar
    Garry Blankenship Guest

    Default Re: Scorched grounding lug

    Quote Originally Posted by John Kogel View Post
    My point is that hot spots were caused by this flaky connection. Square D provides mounting holes for these ground lugs up the sides of the panel.
    Unlikely the schorches have anything to do with those ground wires John. They are insurance wires that only carry current in the event of a problem, which is rare. All those wires are bare, so no neutral wires. Many possibilities, but unless there was a fault already in play, those burns were caused by a hot that got away from somebody or by someone doing it for sport. As a young "lectrishun" on a weekend side job, I had to listen to the client complain about how expensive electricians are. Being on a ladder @ that time, I shorted out a hot wire in the box I was working on which made a mini spark show for him before the C/B tripped. He finally shut up and let me work.


  9. #9
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Scorched grounding lug

    I suspect that a hot got pinched or cut when the KO was made.

    All answers based on unamended National Electrical codes.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •