Water Heater Attachment
Can anyone tell me what this flue type device is on the side of the water heater. I could not find any source of power on it.
Similar Threads:
-
02-05-2012, 07:42 PM #2
Re: Water Heater Attachment
From the looks of it ... it looks like a Git-R-Done-yourself direct vent.

-
02-05-2012, 08:39 PM #3
Re: Water Heater Attachment
Thanks, Jerry. I always appreciate your comments.
-
02-05-2012, 09:08 PM #4
Re: Water Heater Attachment
By the way, I don't see a sediment trap installed on the right water heater, and I don't see one installed to serve both water heaters either.
The photo does not show where one would be present at the left water heater either.
-
02-05-2012, 09:12 PM #5
Re: Water Heater Attachment
Yes, I reported the missing sediment traps.
-
02-05-2012, 11:09 PM #6
Re: Water Heater Attachment
Some heat exchangers vent from the bottom of the tank. However I've only seen this in condensing units. Not sure how this could work without a power vent.
A.O. Smith Vertex Water Heaters: An Overview - YouTube
-
02-05-2012, 11:13 PM #7
Re: Water Heater Attachment
That would be a combustion air duct. The vent goes up through the center to heat the water. Otherwise, it would get no combustion air, since it is sitting flat on the base. They also need drain pans, since they are sitting on a wood structure. I also don't see the bonding jumper on the csst gas line.
Last edited by Scott Cook; 02-05-2012 at 11:43 PM.
-
02-06-2012, 05:45 AM #8
Re: Water Heater Attachment
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
02-06-2012, 05:53 AM #9
Re: Water Heater Attachment
Tank looks like a Bradford White. Any pics of the top of the tank?
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
-
02-06-2012, 06:48 AM #10
-
02-06-2012, 06:50 AM #11
Re: Water Heater Attachment
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
02-06-2012, 07:33 AM #12
Re: Water Heater Attachment
John,
Thanks, I'll have to study up on that.
They do appear to be direct vent configuration with a concentric vent pipe leaving the top to the unit. It looks like a factory made unit, the brand and model number would be needed to look it up. See drawing on page 38. http://www.google.com/url?sa=t&rct=j...akesOF3wMhQxcQ
Last edited by Scott Cook; 02-07-2012 at 06:35 AM. Reason: Better drawing on page 38
-
02-06-2012, 01:29 PM #13
Re: Water Heater Attachment
Although it is obvious, you might want to add that the discharge pipe for the one temperature/pressure relief valve that we can see, doesn't go to the floor, the other valve that appears to be in the right rear corner is probably ready to squirt on the wall. Nice access for testing.
-
02-06-2012, 05:31 PM #14
Re: Water Heater Attachment
-
02-06-2012, 07:37 PM #15
Re: Water Heater Attachment
No drain pans protecting the wood support platform and I'll bet there was no electrical bonding jumpers either? As I've said far to many times before a residential water heater is probably the richest appliance in reportable defects.
Jerry McCarthy
Building Code/ Construction Consultant
-
02-07-2012, 06:51 AM #16
Re: Water Heater Attachment
Kyle,
You can only vent exhaust gases from the bottom of a vertical heater if you have a power vent (fan forced) draft, since a natural draft requires the heat to travel upward through the water heat exchanger tube. The fan can be in the vent pipe (induced) or in the combustion air inlet (forced), but this has neither. So it would be a natural draft direct vent.
See drawing on page 38 for the heater style in the OP's photo. http://www.google.com/url?sa=t&rct=j&q=what+is+direct+vent+water+heater& source=web&cd=1&ved=0CGUQFjAA&url=http%3A%2F%2Fwww .bradfordwhite.com%2Fimages%2Fshared%2Fpdfs%2Fmanu als%2F238-42498-00K.pdf&ei=fOUvT_2gEsKA2wWF3OnUAw&usg=AFQjCNGDQU55 51JldQg312p1s6a3jj70vg&sig2=y0SsMLbVakesOF3wMhQxcQ
Last edited by Scott Cook; 02-07-2012 at 07:26 AM. Reason: clarification
-
02-07-2012, 07:40 AM #17
-
02-07-2012, 10:43 AM #18
Re: Water Heater Attachment
Take another good look Vern. That red whatever I'm sure is not Pex piping and the gas supply piping sure looks like plain old metal???? so.......................
Oh ya, one of the two water heaters eventually leaks, rots the wood platform, the weight of 2 water heaters collapses the platform, the gas lines tear lose, bla, bla, bla....
And one more thing, the water heater on the right side of the photo was installed so one cannot read the lighting & shut-down labels, or maybe even access the burner or pilot controls?
Jerry McCarthy
Building Code/ Construction Consultant
-
02-07-2012, 10:52 AM #19
Re: Water Heater Attachment
The red whatever may not be PEX, but can you tell if the water pipe is or is not by the picture? Did not know gas pipe needed to have bond jumper
. If one of the water heaters leaks long enough to rot the wood to the point it collapses, the resident has bigger problems with vision loss. I can't tell how far the water heater is from the wall or exactly where the labels are, might be wrong, but I was not asking about that.
The beatings will continue until morale has improved. mgt.
-
02-07-2012, 01:48 PM #20
Re: Water Heater Attachment
I have see them bonded and grounded outside a home. They sometimes use the service equipment enclosure and a ground rod because the gas service was in a non metallic pipe and converted to a metal pipe after the meter.
Vern, if you think about it, even with PEX water piping---a powered vent WH, electronic starters, furnace, dryer, stove, AC is near the conducting gas pipe. Should the water heater or a pipe become live, someone could get hurt as well as a possible explosion. It's important that the metalic gas piping be bonded and grounded. I believe this was discussed in detail, and the reasons why a thread a while back.
-
02-07-2012, 03:36 PM #21
-
02-07-2012, 04:01 PM #22
Re: Water Heater Attachment
Be careful what you ask for Vern......................

2008 NEC 250.104 (B)
Jerry McCarthy
Building Code/ Construction Consultant
-
02-07-2012, 04:31 PM #23
Re: Water Heater Attachment
Vern, don't have any pictures, but you could check in the NFPA 54: National Fuel Gas Code, Chapter 7, Electrical Bonding & Grounding, or you are interested in the plastic covered metalic tubing you could DL the WardFlex Installation Guide at WARDFLEX STEPSAVER. (WARDFLEX STEPSAVER) Both sources should answer any questions that you may have on bonding and grounding gas service. I think there may be some people here may have some pictures.

-
02-07-2012, 04:32 PM #24
-
02-07-2012, 04:36 PM #25
Re: Water Heater Attachment
The beatings will continue until morale has improved. mgt.
-
02-07-2012, 05:10 PM #26
Re: Water Heater Attachment
Page 56; Under line is mine.
"WARDFLEX® CSST installed inside or attached to the exterior of a building or structure shall be
electrically continuous and directly bonded, by a qualified person, to the ground system of the building.
The gas piping is considered to be directly bonded when installed in accordance with the following instructions:
• A bonding jumper is permanently and directly connected to the electrical service grounding system.stream of the gas meter of each individual housing unit within a multi-family structure."
This can be achieved through a connection to the electrical service equipment enclosure, the grounded
conductor at the electrical service, the grounding electrode conductor (where of sufficient size) or to the one or
more grounding electrodes used.
• A single bond connection is made to the building gas piping downstream of the utility meter or second stage
regulator (LP systems), but near the gas service entrance (either outdoors or indoors) of the structure, or dow
There was no picture of this area in the OP.
The beatings will continue until morale has improved. mgt.
-
02-07-2012, 05:36 PM #27
Re: Water Heater Attachment
Vern,
Careful of your choice of wording there ... the "grounded" conductor *should not be bonded to anything* after the service equipment, and the only thing the "grounded" conductor is bonded to at the service equipment is the "grounding" conductor, either at a terminal or through a bonding jumper tying the neutral terminal bar to the enclosure, which is then tied to the grounding conductor.
-
02-07-2012, 05:42 PM #28
Re: Water Heater Attachment
Vern,
Why does it matter "how many people are living in that finished space below the water heater"?
From the IRC: (bold and underlining is mine)
- P2801.5 Required pan. Where water heaters or hotwater storage tanks are installed in locations where leakage of the tanks or connections will cause damage, the tank or water heater shall be installed in a galvanized steel pan having a minimum thickness of 24 gage (0.016 inch) (0.4 mm) or other pans for such use. Listed pans shall comply with CSA LC3.
There is no reference to being above living space in there.
-
02-07-2012, 06:35 PM #29
-
02-07-2012, 08:09 PM #30
Re: Water Heater Attachment
Rich, you're right. The building codes are the bible that governs our industry and we need to know and thoroughly understand them and those that ignore, reject or do not understand them occupy their own bubble of rejection (ignorance) and will eventually suffer the consequences.
Jerry McCarthy
Building Code/ Construction Consultant
-
03-04-2012, 07:30 PM #31
Re: Water Heater Attachment
How about the T&P drain pipes and no seismic straps.
-
03-05-2012, 06:00 AM #32
Re: Water Heater Attachment
That is a direct vent water heater. It has its own air supply brought in from either outside of the confined space or directly from outside the home. They are used primarily in a confined space where adequate combustion air is not available. They are also used in highly energy efficient homes where air infiltration can be of concern.
http://www.bradfordwhite.com/images/..._dv_1004_a.pdf
Last edited by Travis Lea; 03-05-2012 at 06:07 AM. Reason: link added
-
07-25-2012, 11:10 PM #33
Re: Water Heater Attachment
Hi
I agree with you Jerry.