Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default csst separation issue

    Is it ok to have the csst laying all over the electrical cables? I know you're supposed to have as much separation as possible from electrical conductive systems....seems like they didn't even try....

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: csst separation issue

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: csst separation issue

    Thanks Jerry....what do you think about the separation issue?


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: csst separation issue

    Quote Originally Posted by Ray Thornburg View Post
    Thanks Jerry....what do you think about the separation issue?
    From that other thread:
    Quote Originally Posted by Jerry Peck View Post
    The best reference would be that it is not properly secured and supported as required ... but the insulation on the conductors within the outer sheath should provide protection from any electrical problem from the two being in contact with each other.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: csst separation issue

    I know I thought about that too.....but the csst manual says as much separation as possible from electrically conductive systems.....and since the electric is a system....it just seems they didn't follow the intent manual when they could easily have routed it some other way.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: csst separation issue

    Quote Originally Posted by Ray Thornburg View Post
    the csst manual says as much separation as possible from electrically conductive systems ...
    True, but how much is as much as possible? It is "possible" to route the electrical wiring on one side of the house and the CSST on the other side of the house, right?

    I agree that saying things like 'as much as possible' is rather useless because, one 'could' run the electrical half-way around the earth from the CSST (an extreme example, but that is 'as much as possible'). Saying 'as much as possible' could mean 'let's use *real* pipe and replace the CSST with iron pipe'.

    Thing like that in manuals are really kind of silly when you consider that the CSST is routed across the attic and down walls, and electrical cables are also routed in those same places. It would be nice if the code or installation instructions said 'minimum separation between CSST and electrical wiring, light fixtures, and other electrically energized appliances is 3 inches', but I have not seen any such requirements ... as yet ... not sure if they will come in the future or not, especially with CounterStrike CSST with its outer sheath which is supposed to eliminate the additional bonding that regular CSST requires for lightning strike protection.

    I found these interesting in the GasTite Design and Installation Guide: (bold and underlining are mine)
    - NATIONAL ELECTRIC CODE (NEC), Section 250.104b, states that “bonding all piping and metal air ducts within the premises will provide additional safety”. Gastite recommends that all continuous metallic systems be bonded and grounded. The owner should confirm with an electrical or construction specialist that each continuous metallic system in a structure has been bonded and grounded by an electrical professional in accordance with local building codes. This should include, but is not limited to metallic chimney liners, metallic appliance vents, metallic ducting and piping, electrical cables, and structural steel.

    - Care should be taken when installing horizontal runs to maintain as much separation as reasonably possible from other electrically conductive systems in the building.
    * - There is no requirement to maintain separation from other electrically conductive systems when routing FlashShield™.

    * As though there was a stated "requirement" of a specific minimum separation for regular GasTite CSST in the statement above it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: csst separation issue

    Thanks Jerry....so the bottom line is cheesy but legal.....would you mention it in a report? Just interested in how other inspectors handle stuff like this.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: csst separation issue

    Quote Originally Posted by Ray Thornburg View Post
    so the bottom line is cheesy but legal...
    Yep.

    ... would you mention it in a report?
    Nope.

    But I would be curious as to what that OSB wall is covered for and if that hole should be sealed around.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: csst separation issue

    The lines emerge into another attic area.....the plywood is a type of shear wall in the attic to brace the trusses for the wind zone around here.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •