Re: Siemens breakers in Sqare D panel ill fitting
Mark,
You will find this condition on older service panel, normally when AC is replaced, pool addition, or other modifications that require a breaker to be added or changed. Rather than plan ahead to make sure they have the correct breaker, they grab whatever breaker they have in their truck. Whatever the cause it is not OK and does not meet code. If you look at the manufacturer label it will list what breakers are acceptible, which will be only their breakers. Below is verbage in my report:
Incompatible breakers are noted, normally, when an electrical panel manufacturer have their panel tested for UL approval, the test will be conducted using only the manufacturer's breaker. For this reason, the manufacturer will advise that only their breakers should be used in their panel. Industry standards require that equipment shall be installed and used in accordance with any instructions included in the listing or labeling. Several other brand breakers have been installed and therefore does not meet industry standards.
1997 National Electrical Code 110-3 (b) Listed and labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
-
07-10-2013, 05:03 PM #3
-
07-13-2013, 09:24 PM #4
Re: Siemens breakers in Sqare D panel ill fitting
The link shown is for Eaton products, not Siemens.
-
07-13-2013, 10:06 PM #5
Re: Siemens breakers in Sqare D panel ill fitting
-
07-14-2013, 06:43 AM #6
Re: Siemens breakers in Sqare D panel ill fitting
Still a list of Eaton products classified for other makes, CHQ is the Eaton/Cutler-Hammer classified replacement for SQ D QO. I cannot think of what Siemens calls their UL classified QO replacement, but would love to see a list, if any, of Siemens breakers classified for other makes, SQ D Homeline is not classified for any other makes.
-
07-14-2013, 08:51 AM #7
Re: Siemens breakers in Sqare D panel ill fitting
"Get correct views of life, and learn to see the world in its true light. It will enable you to live pleasantly, to do good, and, when summoned away, to leave without regret. " Robert E. Lee