Results 1 to 4 of 4
Thread: Code for vent pipe slope
-
02-02-2013, 04:43 PM #1
Code for vent pipe slope
Believe it or not the seller says she will fix a negative sloping furnace vent pipe connector only if I can provide the code for it. I do not recite codes in my reports but use diagrams to illustrate the 1/4 inch per foot slope upward away from the furnace. I'm sure someone here knows it off the top of their head. Thanks for the help.
Similar Threads:
-
02-02-2013, 05:10 PM #2
Re: Code for vent pipe slope
IRC
G2427.10.8 (503.10.8) Slope. A vent connector shall be installed without dips or sags and shall slope upward toward the vent or chimney at least 1/4 inch per foot (21 mm/m).
Exception: Vent connectors attached to a mechanical draft system installed in accordance with the appliance and draft system manufacturers’ instructions.
Last edited by Mark Hagenlock; 02-02-2013 at 05:15 PM. Reason: clarification
-
02-02-2013, 05:18 PM #3
Re: Code for vent pipe slope
IRC M1803.3 ...Connectors shall be as short and straight as
possible and installed with a slope of not less than 1/4 inch (6 mm)
rise per foot of run....
-
02-03-2013, 11:57 AM #4
Re: Code for vent pipe slope
Thanks again



Reply With Quote