Can second (non-service) panel GEC be the second GEC?
As I understand it, there should be a secondary GEC when the primary GEC is not connected to a UFer.
The house I saw today had only one GEC in the main panel and there was a GEC in the panel in the garage. Since there are two GECs in this system, is the requirement met, or does there need to be two at each panel?
I would think that it's fine the way it is, but wanted to get some more experienced perspective.
-
08-10-2013, 03:58 AM #2
Re: Can second (non-service) panel GEC be the second GEC?
What type of electrodes were used? Was the garage attached or detached?
All answers based on unamended National Electrical codes.
-
08-10-2013, 04:55 AM #3
-
08-10-2013, 06:51 PM #4
Re: Can second (non-service) panel GEC be the second GEC?
Ah, so the same GEC could possibly be attached to two electrodes, and therefore I might only see one GEC terminating at the panel, correct? I was thinking that each electrode needed it's own GEC to the panel.
In this case I don't know what type of electrodes were used, as I didn't dig down to find them; I only saw the GECs entering the ground. I am assuming rods.
-
08-11-2013, 09:07 AM #5
-
08-17-2013, 05:15 AM #6
Re: Can second (non-service) panel GEC be the second GEC?
Just a side issue. If there are two or more grounding electrodes, such as one in the house and one in the garage, and they are not bonded----due to soil or local environmental conditions (close to a sub-station as an example), you may have current flowing between them. This may cause "noise" in electronic devices and possibly a shock, should you somehow happen to get between the individual electrode grounds.