12-23-2013, 06:30 PM #1
-
12-23-2013, 06:36 PM #2
Re: Sink drain
Hi Richard,
Shown is a bottle trap. KOHLER | K-9033 | Contemporary Round Bottle Trap
* several installation instructions on line.
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
12-23-2013, 06:41 PM #3
-
12-23-2013, 07:07 PM #4
Re: Sink drain
That is a bottle trap
No, it is not installed correctly
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
12-27-2013, 12:06 AM #5
Re: Sink drain
As installed it amounts to an s-trap which is not allowed under current code. The trap arm should be at level with the inlet to the wall t.
-
12-27-2013, 04:21 AM #6
Re: Sink drain
That can be really useful , especially if you have kids like mine who used to throw their Popsicle sticks into the sink (of course the sticks would go down the drain) With a price tag of $ 140 that is a very pricey trap ...... and yes it was installed wrong , but I did want to point out how useful it could be. Beats taking a p-trap apart , just drop the bottle and get the sticks out.
-
12-28-2013, 10:50 AM #7
Re: Sink drain
It is stated that the install is not correct, does anyone have a picture or link to see a correctly installed unit?
-
12-28-2013, 11:05 AM #8
Re: Sink drain
I don't have a photo with me, however, you see the horizontal pipe coming out of the trap and it turns down - that should not turn down, it needs to slope down slightlyto vent stack, but if the pipe were to fill with water to the overflow of the trap (trap weir) the water would not be high enough to block the vent.
-
12-28-2013, 04:47 PM #9
Re: Sink drain
So the tail piece from the sink needs to be longer so the pipe from the side of the trap runs with slight fall to the sanitary tee in the wall. So I assume there is some kind of baffle in the trap to make the trap hold water to stop sewer gas? Looks like this would hold sediment after a while and need cleaning? Thanks for you comment Jerry.
-
12-28-2013, 04:52 PM #10
Re: Sink drain
Last edited by Jerry Peck; 12-28-2013 at 05:17 PM. Reason: added touched up photo
-
12-30-2013, 08:21 AM #11
Re: Sink drain
There is an internal partition like this drawing shows:

You might want to check your area to see if they are allowed. They are not allowed around here.
Yes, you can extend the tailpiece down, but there is a limit to how far down, I know in WI it's 15 inches, in other areas it can be 24 inches.
-
02-17-2014, 04:02 PM #12
Re: Sink drain
Prohibited in Canada under the 2010 plumbing code.
-
02-17-2014, 08:19 PM #13
Re: Sink drain
Bottle traps are against most codes. It is defiantly against the Illinois Plumbing code. Part d say there is to be no partitions which is how a bottle trap works, so it is a prohibited trap.
Section 890.410 Fixture Traps/Continuous Waste
d) Type of Traps. Traps shall have a uniform and smooth interior, and shall have no partitions or movable parts. The trap seal shall be non-adjustable.
k) Prohibited Traps. Use of the following traps is prohibited (see Appendix D: Illustration E):
1) Traps which depend upon the action of movable parts for their seal.
2) Full "S" traps. Exception: Water closet and similar fixtures which depend on self-siphonage for their proper operation.
3) Bell traps.
4) Crown vented traps.
5) Unvented running traps.
6) Fixtures with concealed interior partitioned traps. Exception: Fixtures with integral traps constructed of vitrified earthenware and penal institutional fixtures with integral traps constructed of ferrous material.
Ron Hasil IL Plumbing Lic #058-160417
A-Archer Sewer & Plumbing specializing in: