Results 1 to 4 of 4
  1. #1
    Christian Tag's Avatar
    Christian Tag Guest

    Default Furnace register

    Hi everyone,

    Is it recommended to have a Furnace supply on the garage ceiling ? Isn't there a risk for the carbon monoxide to get in the house ? I usually see a normal electric baseboard in a garage.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Furnace register

    Quote Originally Posted by Christian Tag View Post
    Hi everyone,

    Is it recommended to have a Furnace supply on the garage ceiling ? Isn't there a risk for the carbon monoxide to get in the house ? I usually see a normal electric baseboard in a garage.
    Not Allowed in the Garage.

    *taken from IRC 2006

    R309.1.1 Duct penetration. Ducts in the garage and ducts
    penetrating the walls or ceilings separating the dwelling from
    the garage shall be constructed of a minimum No. 26 gage
    (0.48 mm) sheet steel or other approved material and shall have
    no openings into the garage.




    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: Furnace register

    I write it up as a safety hazard not only for CO gas but it breeches fire separation requirements. Even if there is not living space above the garage, the garage is also supposed to be separated from its attic space by appropriate fire rated materials. By appropriate I mean whatever the local jurisdiction requires. And if the local does not apply, I refer to the IRC.

    - - - Updated - - -

    Here is is R309.2

    http://publicecodes.cyberregs.com/icod/irc/2003/icod_irc_2003_3_par082.htm


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Furnace register

    As previously stated - no openings to the garage ... from the system serving the house, the garage is permitted to have its own system with its own openings.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •