Results 1 to 10 of 10
  1. #1
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Pool lights and GFCI protection

    Hi, need to learn about below water line pool lights and GFCI protection.
    Questions:
    (1) I know that 120v lights should have it but not sure about more modern lights that are low voltage
    (2) If low voltage lights require it; when did that go into effect by the NEC
    Thanks

    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Pool lights and GFCI protection

    The power supply to the transformer can be GFCI protected but once the power is stepped down (pool side) you do not have the protection of the GFCI. I do not know of a GFCI protection for low voltage, as far as I know GFCI is only for 120v.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by Scott Patterson View Post
    The power supply to the transformer can be GFCI protected but once the power is stepped down (pool side) you do not have the protection of the GFCI. I do not know of a GFCI protection for low voltage, as far as I know GFCI is only for 120v.
    Scott, thanks. Next question; by the 2008 NEC; will a modern pool with low voltage light still require GFCI protection to the transformer?


  4. #4
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by mark petty View Post
    Scott, thanks. Next question; by the 2008 NEC; will a modern pool with low voltage light still require GFCI protection to the transformer?
    What does the 2008 NEC say?

    Most of the places in my area are on the 2012 NEC.

    I don't inspect pools, most of the pools in the homes I inspect cost as much or more than my $200k home! I tell my clients to contact a pool specialist, just too many things to keep up with and the liability with pools is so great I just do not want to mess with them. I know that in many areas the home inspector is expected to inspect the pool, I'm glad that is not the case in my area.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Pool lights and GFCI protection

    From the 2008 NEC: (underlining is mine)
    - 680.23 Underwater Luminaires.
    - - This section covers all luminaires installed below the normal water level of the pool.
    - - (A) General.
    - - - (3) GFCI Protection, Relamping. A ground-fault circuit interrupter shall be installed in the branch circuit supplying luminaires operating at more than 15 volts such that there is no shock hazard during relamping. The installation of the ground-fault circuit interrupter shall be such that there is no shock hazard with any likely fault-condition combination that involves a person in a conductive path from any ungrounded part of the branch circuit or the luminaire to ground.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by Jerry Peck View Post
    From the 2008 NEC: (underlining is mine)
    - 680.23 Underwater Luminaires.
    - - This section covers all luminaires installed below the normal water level of the pool.
    - - (A) General.
    - - - (3) GFCI Protection, Relamping. A ground-fault circuit interrupter shall be installed in the branch circuit supplying luminaires operating at more than 15 volts such that there is no shock hazard during relamping. The installation of the ground-fault circuit interrupter shall be such that there is no shock hazard with any likely fault-condition combination that involves a person in a conductive path from any ungrounded part of the branch circuit or the luminaire to ground.
    Jerry, thanks
    Does this mean - or - do most / all modern pools have lights 15 volts or less


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by mark petty View Post
    Jerry, thanks
    Does this mean - or - do most / all modern pools have lights 15 volts or less
    Mark,

    Most are 12 volts.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by Jerry Peck View Post
    Mark,

    Most are 12 volts.
    Jerry, thanks again


  9. #9
    Join Date
    Nov 2010
    Location
    California
    Posts
    97

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by Scott Patterson View Post
    as far as I know GFCI is only for 120v.
    240 volt for pump motors is also available.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Pool lights and GFCI protection

    Quote Originally Posted by Scott Patterson View Post
    ... as far as I know GFCI is only for 120v.
    Quote Originally Posted by David Bertrams View Post
    240 volt for pump motors is also available.
    Scott was answering the question about GFCI protection for pool lights, I haven't seen any 240 volt pool lights.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •