    Default Combustion air vent

    Last edited by Clay White; 12-26-2007 at 11:13 AM.
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Combustion air vent

    Quote Originally Posted by Clay White View Post
    what would possess the HVAC contractor to install the combustion air vent adjacent to the gas meter....yikes, bad move!

    Especially when it should be 3 feet away!

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Jul 2007
    Location
    new hampshire
    Posts
    17

    Default Re: Combustion air vent

    There is a screen over the relief vent on the regulator . If it is popped out the hole is treaded . The vent can be piped away to meet the Three, Four or Five foot requirement , Depending who you talk to ......

    That regulator sure is not in the best location ...