Results 1 to 10 of 10
  1. #1
    Join Date
    Jul 2014
    Location
    CA
    Posts
    5

    Default Hearth extension code?

    I was wondering what the hearth extension code is for a raised factory built fireplace. The bottom of the firebox is 2 feet from the combustible flooring. Thanks.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Robert W; 01-11-2015 at 10:31 PM.
    Member Benefits1

  2. #2
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Hearth extension code?

    NFPA 211

    11.3.2 The minimum thickness of hearth extension shall be
    2 in. (51 mm).
    11.3.3 Where the fireplace opening is less than 6 ft2 (0.56 m2),
    the hearth extension shall extend as follows:
    (1) At least 16 in. (406 mm) in front of the facing material
    (2) At least 8 in. (203 mm) beyond each side of the fireplace
    opening (See Figure 11.3.3.)
    11.3.4 Where the fireplace opening is 6 ft2 (0.56 m2) or
    larger, the hearth extension shall extend as follows:
    (1) At least 20 in. (508 mm) in front of the facing material
    (2) At least 12 in. (305 mm) beyond each side of the fireplace
    opening (See Figure 11.3.3.)
    11.3.5 Where a fireplace is elevated above or overhangs a
    floor, the hearth extension also shall extend over the area under
    the fireplace.



  3. #3
    Join Date
    Jul 2014
    Location
    CA
    Posts
    5

    Default Re: Hearth extension code?

    Thanks Marc. You're the man.


  4. #4
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,871

    Default Re: Hearth extension code?

    Quote Originally Posted by Robert W View Post
    Thanks Marc. You're the man.
    Just looking out for my boys in CA


  5. #5
    Join Date
    Jun 2010
    Location
    San Luis Obispo
    Posts
    26

    Default Re: Hearth extension code?

    Quote Originally Posted by Marc M View Post
    NFPA 211
    NFPA 211 is good stuff, however that is a factory fireplace and the instructions will list the hearth requirements for that unit including the ember strip 1/2 under the fireplace, 1/2 under the hearth.

    In my area of CA that unit would also need glass doors.


  6. #6
    Mark Sokalski's Avatar
    Mark Sokalski Guest

    Smile Re: Hearth extension code?

    Quote Originally Posted by Marc M View Post
    NFPA 211

    11.3.2 The minimum thickness of hearth extension shall be
    2 in. (51 mm).
    11.3.3 Where the fireplace opening is less than 6 ft2 (0.56 m2),
    the hearth extension shall extend as follows:
    (1) At least 16 in. (406 mm) in front of the facing material
    (2) At least 8 in. (203 mm) beyond each side of the fireplace
    opening (See Figure 11.3.3.)
    11.3.4 Where the fireplace opening is 6 ft2 (0.56 m2) or
    larger, the hearth extension shall extend as follows:
    (1) At least 20 in. (508 mm) in front of the facing material
    (2) At least 12 in. (305 mm) beyond each side of the fireplace
    opening (See Figure 11.3.3.)
    11.3.5 Where a fireplace is elevated above or overhangs a
    floor, the hearth extension also shall extend over the area under
    the fireplace.

    Chapter 11.1 of NFPA 211 applies to Factory-built fireplaces: 11.1.2 " Hearth extensions shall be provided in accordance with the manufacturer's instructions or shall be of masonry or on-combustible construction in accordance with Section 11.3 (see above). [manufacturer's instructions always take precedence over the code.]


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Hearth extension code?

    Quote Originally Posted by Mark Sokalski View Post
    [manufacturer's instructions always take precedence over the code.]
    Not if the code is more restrictive.

    The codes reference the code AND the manufacturer's installation instructions, which means the most restrictive of the two apply.

    Mamy (most) codes state "the most restrictive" shall apply, and "this code and the manufacturer's installation instructions" and even something similar to 'unless the manufacturer's installation instructions violate this code, then the code shall apply'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    May 2010
    Location
    No. San Diego Co., CA
    Posts
    562

    Default Re: Hearth extension code?

    Haven't done the inspection yet, that's tomorrow so I can't post my own pic. However, looking at the OPs pic and from what I can see with listing pics, the fireplace looks very similar, I.e factory built and elevated 18" or so. The differences being that with tomorrow's challenge, the fireplace has glass doors and the floor directly below them is tile, as is the whole of the ground floor. The hearth itself is not raised but also of a non-combustible material - floor tile but set on a diagonal to differentiate from the rest of the floor. I'm of the opinion that it still does not negate the requirement for a raised hearth.

    This is a 2006 tract home, without modification (I'm told) and clearly passed AHJ final occupancy inspection and approval. Thoughts?


  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Hearth extension code?

    Quote Originally Posted by Ian Page View Post
    Haven't done the inspection yet, that's tomorrow so I can't post my own pic. However, looking at the OPs pic and from what I can see with listing pics, the fireplace looks very similar, I.e factory built and elevated 18" or so. The differences being that with tomorrow's challenge, the fireplace has glass doors and the floor directly below them is tile, as is the whole of the ground floor. The hearth itself is not raised but also of a non-combustible material - floor tile but set on a diagonal to differentiate from the rest of the floor. I'm of the opinion that it still does not negate the requirement for a raised hearth.

    This is a 2006 tract home, without modification (I'm told) and clearly passed AHJ final occupancy inspection and approval. Thoughts?
    If it has a glass panel covering the front of the fireplace with direct vent gas logs, the hearth is a non-issue. The NFPA 211 was primarily written to cover wood burning fireplaces, where logs, embers, etc could fall out of the opening….. Sometimes common sense needs to win…

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    Join Date
    May 2010
    Location
    No. San Diego Co., CA
    Posts
    562

    Default Re: Hearth extension code?

    Having a hard time posting a pic...but anyway, the fire box and hearth is s I first saw. A Superior fire box, capable of handling logs and other flamables with bi-fold glass doors (not fixed as they would be for a vented gas log set) and a mesh spark screen. Hearth is level with surrounding tile floor and not raised. Any extensions, as required, is thereby moot. Firebox is 16" above tile.
    Definately a hazard to young'uns, walking into the fire when lighted.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •