Results 1 to 4 of 4

Thread: Neutral SEC

  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default Neutral SEC

    Last edited by Jeff Eastman; 12-19-2007 at 02:38 PM.
    Member Benefits1

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Neutral SEC

    It is fine being bare as long as it is the service.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Neutral SEC

    James is correct ...

    Because that is "service entrance conductor" and is serving as both the "groundING" and the "groundED" conductor, that is not required to be insulated. However, from the service equipment on, the neutral is required to be insulated.

    That bend, though, is too sharp, but I would not necessarily want to un-bend it and re-bend it now.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Neutral SEC

    Jeff

    The area between the 2 15 amp breakers and tied together breakers looks discolored.

    Was there an indication of sparking or heat build up ?

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •