Results 1 to 11 of 11
    Default NEC Bonding Article
    Neutral and equipment ground can only be bonded together at the service equipment. I was trying to find the specific article. Right now, my brain is muddy and I am (for some reason) unable to decipher clearly. Is this the correct reference?
    From 2017 NFPA 70 (NEC)
    250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
    (B) Load-Side Equipment. Except as permitted in 250.30(A)(l) and 250.32(B) a grounded circuit conductor shall not be used for grounding non-current-carrying metal parts of equipment on the load side of the service disconnecting means or on the load side of a separately derived system disconnecting means or the overcurrent devices for a separately derived system not having a main disconnecting means.
    Default Re: NEC Bonding Article
    Yes.
    ... shall not be used for grounding non-current-carrying metal parts of equipment on the load side of ...
    Yes.
    Thanks Jerry,
    I hope you are doing well.
    Mar 2013
    Md and or PA
    250.142
    Is for using the grounded ( neutral) for the grounding ( ground) conductor on the load side of the service.This is what was done for years for 3 wire ranges and dryers.
    My first thought when I read your post was 250.24. Which is the article explaining the 3 locations the grounding electrode conductor is permitted to be connected to the grounded service conductor ( neutral)
    I am curious as to exactly what it is you are looking for ? An equipment ground ( branch circuit ground) or the grounding electrode conductor ( service)
    Quote Originally Posted by jack davenport View Post
    250.142
    Jack,
    I was looking for where the grounded and grounding conductors are to be bonded together. Looks like 250.24 (A)(5) & (B) also covers that.
    That is, if I am reading this correctly. Right now, I have a head cold. Might explain why I was having trouble yesterday.
    MONTREAL QUEBEC-CANADA
    Jack,
    In most cases, bonding / grounding takes place at the main service equipment panel.
    Here is a PDF. Hope it helps. http://www.homeinspector.org/files/i...ts/Alquist.pdf
    Get better soon.
    Best.
    Robert
    Har har. A comedian. Just what I needed.
    Not making a funny, Gunner.
    "So Sorry" if it seemed that way. Not intended.
    As to your question, "I was looking for where the grounded and grounding conductors are to be bonded together." I took it literally.
    I have, as well as many, have been known to come up empty at times, brain fart, blank, reclusing myself/themselves from what I, they know, knew, momentarily drawing a blank/s.
    Not fun but it is what is is.
    Hope you get well soon.
    Robert,
    I found it funny because you sent me my own Grounding & Bonding presentation back to me.
    I try to be thoughtful.
    Gunnar,
    I think Robert is missing what you are saying.
Tags for this Thread
